Results 1 to 9 of 9
Thread: Clivet chiller
-
02-03-2009, 12:53 PM #1
Clivet chiller
hi,
i am finding it very difficult to get any useful info on clivet chillers..has anybody got the fault codes at least? i am getting E01 and E31, the model in WRAT-242.....
rgrds phil
-
02-03-2009, 08:01 PM #2
Re: Clivet chiller
Hi!
What is the controller model?
-
22-03-2009, 09:32 AM #3
Re: Clivet chiller
Phil
just seen this, if we are talking about the model with a red led readouts (3 digit and 2 digit) then E01 is hp trip circuit 1, e31 not shown in my book but an E21 is hp trip circuit 2 and e41 flow alarm on water side hope this helps
andy
-
22-03-2009, 02:47 PM #4
Re: Clivet chiller
These codes corespond to a CVM 2 controller on a WRAT Climavenita chiller. Sure its not a Climavenita chiller? Cheers Kev.
In the words of David Byrne, Well...How did I get here?
-
22-03-2009, 03:20 PM #5
-
23-03-2009, 06:10 AM #6
Re: Clivet chiller
Nice Clivet site
Clivet
-
23-03-2009, 07:32 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
24-03-2009, 05:53 AM #8
Re: Clivet chiller
Good Link
Thanks Narkom
Grizzly
-
21-05-2009, 08:57 AM #9
Re: Clivet chiller
E01-Evaporator antifreeze alarm-check the water flow and the probe resistance bydisconnecting it to its terminals.
E31-Module 1 off network- check the serial addresing card.
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
Absorption Chiller VS Mech. Chiller
By Intern in forum IndustrialReplies: 20Last Post: 30-05-2009, 08:31 AM -
york chiller motor rotation error
By cesarnino in forum Trouble ShootingReplies: 7Last Post: 13-12-2008, 03:43 PM -
Clivet chiller
By texanul in forum IndustrialReplies: 2Last Post: 14-11-2008, 09:56 PM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM