Hi All,
How to convert refrigerant load to elect load.
Say eg: from 2,400,000btu/hr to kw.
Thanks & Regards
-
23-03-2009, 02:05 AM #2
Re: Refrigerant load to elect load
Have you read up on the term:
COP = coefficient of performance ?
-
23-03-2009, 05:55 AM #3
Re: Refrigerant load to elect load
no have not read that.
just want to find out the power consumsion.
-
23-03-2009, 08:22 PM #4
Re: Refrigerant load to elect load
Sparo, your laizy, google on to Wikipedia and type C.O.P ,coifficient of performance, and you get all the info you want.
laizy bom, Ice
-
23-03-2009, 09:21 PM #5
Re: Refrigerant load to elect load
2.4m BTU -that's a fair old tonnage!
(Just to confuse things further ;-)
-
18-05-2009, 07:15 PM #6
-
18-05-2009, 07:21 PM #7
Re: Refrigerant load to elect load
^ but that is not the electrical consumption required which was his question.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
19-05-2009, 02:12 AM #8
Re: Refrigerant load to elect load
Just commissioning 2 chillers in Minnesota at 5.5M BTU/hr each. had to convert everything to kW ref load to BTU and C to F time the americans joined the rest of the world and used SI i say.
-
19-05-2009, 01:01 PM #9
Re: Refrigerant load to elect load
240,0000 btu/hr = 200 TR
2OO TR DIVIDED BY 0.2845 = 702.98 KW
-
19-05-2009, 01:54 PM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
19-05-2009, 08:21 PM #11
Re: Refrigerant load to elect load
I use such, however, a very, very rough conversion: 1000 W electrical = 3000 W heat = 9000 Btu (also "heat", of course), simply, a mnemonic: 1-3-9, and vice versa.
-
19-05-2009, 08:30 PM #12
Re: Refrigerant load to elect load
This concerning the choice of a comp for an AC. I believe, I have not confused the numbers unforgivably.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
MHI FDCA400HKXRE4 Tech Info Please
By L.JT in forum Trouble ShootingReplies: 5Last Post: 23-08-2008, 11:00 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM