Calculating the needed water temperature for a coil
Hey everybody!
Let me get straight to the point:
I have a coil that uses chilled water too cool down air to a given temperature. The average apparature dew point is 13 degrees celsius.
Now based on the specs of coil and air, my job is to calculate the incoming and outgoing temperature of the chilled water (flow etc. is known).
Can you provide me with formulas or programs, or maybe just some advices which direction to go?
Thanks a lot in advance!
aztec
PS: Nice forums you have here...
-
13-05-2009, 03:26 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Calculating the needed water temperature for a coil
What is dry bulb temperature or humidity
What is water flow? What is desired cooling capacity? What is air flow?
-
18-05-2009, 07:58 AM #3
Re: Calculating the needed water temperature for a coil
Coil Model:
Typical (1/2" Tube)
914 x 2300 4r 14f 8c
Air:
Barometer: 101.325 kPa
Altitude: 0m
Airflow: 7m³
On Coil: 30.0/19.0 ºC
OffCoil: 21.8/16.2 ºC
Cond Rate: 0 g/s
Pressure Drop: 0.198 kPa
Water:
Flow: 0.867 l/s
Velocity: 0.880 m/s
Pressure Drop: 31.5 kPa
Pipe Conn: 35mm
Performance (Dry Surface):
Duty: 67.7 kW
That's all the info I've got. Now based on that, I need the water inlet and leaving temperature.
Thanks a bunch!
-
18-05-2009, 10:41 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Calculating the needed water temperature for a coil
Your water side flow is not good:
ΔT=Q/(m*c)
http://www.refrigeration-engineer.co...ad.php?t=18816
Your ΔT is calculated as 18,65K and is way off of normal values (3-8K).
Your water flow should be around 3l/s.
Than you could calculate with around water in 15°C and water out 20°CLast edited by nike123; 18-05-2009 at 11:12 AM.
Similar Threads
-
Hoshizaki Ice Maker
By Abe in forum Legal-Business-MarketingReplies: 19Last Post: 01-05-2010, 03:27 AM -
cold river water
By eftimios in forum FundamentalsReplies: 8Last Post: 09-11-2008, 06:37 PM -
Efficiency of compressor assisted HRV
By montreal in forum Heat PumpsReplies: 46Last Post: 27-08-2007, 08:51 PM -
temperature difference of evaporator coil
By dantoubiana in forum Trouble ShootingReplies: 12Last Post: 03-05-2003, 03:46 AM -
Calculating Cabinet Temperature?
By mepgkyc in forum Trouble ShootingReplies: 0Last Post: 18-01-2002, 05:16 PM