    Calculating the needed water temperature for a coil



    Hey everybody!

    Let me get straight to the point:
    I have a coil that uses chilled water too cool down air to a given temperature. The average apparature dew point is 13 degrees celsius.
    Now based on the specs of coil and air, my job is to calculate the incoming and outgoing temperature of the chilled water (flow etc. is known).

    Can you provide me with formulas or programs, or maybe just some advices which direction to go?

    Thanks a lot in advance!

    aztec

    PS: Nice forums you have here...



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculating the needed water temperature for a coil

    What is dry bulb temperature or humidity
    What is water flow? What is desired cooling capacity? What is air flow?

  3. #3
    aztec's Avatar
    aztec Guest

    Re: Calculating the needed water temperature for a coil

    Coil Model:
    Typical (1/2" Tube)
    914 x 2300 4r 14f 8c

    Air:
    Barometer: 101.325 kPa
    Altitude: 0m
    Airflow: 7m³
    On Coil: 30.0/19.0 ºC
    OffCoil: 21.8/16.2 ºC
    Cond Rate: 0 g/s
    Pressure Drop: 0.198 kPa

    Water:
    Flow: 0.867 l/s
    Velocity: 0.880 m/s
    Pressure Drop: 31.5 kPa
    Pipe Conn: 35mm

    Performance (Dry Surface):
    Duty: 67.7 kW


    That's all the info I've got. Now based on that, I need the water inlet and leaving temperature.

    Thanks a bunch!

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Calculating the needed water temperature for a coil

    Quote Originally Posted by aztec View Post

    Water:
    Flow: 0.867 l/s
    Velocity: 0.880 m/s
    Pressure Drop: 31.5 kPa
    Pipe Conn: 35mm

    Performance (Dry Surface):
    Duty: 67.7 kW
    Your water side flow is not good:
    ΔT=Q/(m*c)

    http://www.refrigeration-engineer.co...ad.php?t=18816

    Your ΔT is calculated as 18,65K and is way off of normal values (3-8K).

    Your water flow should be around 3l/s.

    Than you could calculate with around water in 15°C and water out 20°C
    Last edited by nike123; 18-05-2009 at 11:12 AM.

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  3. Efficiency of compressor assisted HRV
    By montreal in forum Heat Pumps
    Replies: 46
    Last Post: 27-08-2007, 08:51 PM
  4. temperature difference of evaporator coil
    By dantoubiana in forum Trouble Shooting
    Replies: 12
    Last Post: 03-05-2003, 03:46 AM
  5. Calculating Cabinet Temperature?
    By mepgkyc in forum Trouble Shooting
    Replies: 0
    Last Post: 18-01-2002, 05:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •