Thread: Basic question about recovering
-
12-05-2009, 12:37 PM #1
Basic question about recovering
Hello all,
Im still new to this scene and am Still learning about everything, and would be gratefull of any advise given. Just a few quick questions of things I am a little unsure of:
First of all, When Recovering do I recover just into the vapour valve on the recovery cylinder or liquid? Or do I swap over accordingly?
Also what is the correct way to determine the condenser operating temp? (The unit I am currently working on is a lennox package with R407c.)To work out my pressure test value when leak detecting.
Hope this makes sense, Thanks in advance for any help given
-
12-05-2009, 11:31 PM #2
Re: Basic question about recovering
If you are recovering with a single hose, not doing a push/pull, then it doesn't matter which valve you use. It all ends up in the same place.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
13-05-2009, 07:54 AM #3
Re: Basic question about recovering
Ar Thanks Brian,
Thats what I thought it was just for piece of mind check Im doing the process correctly.
-
13-05-2009, 10:10 AM #4
Re: Basic question about recovering
Hi lees8110,
Also what is the correct way to determine the condenser operating temp? (The unit I am currently working on is a lennox package with R407c.)To work out my pressure test value when leak detecting.
High side with air cooled condenser 55C
High side with evaporative condenser 43C
Low side 32C
So you need to work out the saturation pressure of the refrigerant for those temperatures. Note use the liquid scale on your comparator.Tony
-
13-05-2009, 10:53 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Basic question about recovering
For Fujitsu R407 VRF leak test pressure is 2,94MPa for 24 hours. Change of pressure with temperature is 0,01Mpa/1K
-
14-05-2009, 08:58 AM #6
Re: Basic question about recovering
Spot on tony thanks for that
I remember doing it now,
thanks again
Similar Threads
-
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
basic fridge question
By weidit in forum FundamentalsReplies: 13Last Post: 08-05-2009, 07:52 AM -
r134a question, calculating heat lost by refrigerant
By kamikazi929 in forum FundamentalsReplies: 0Last Post: 03-01-2008, 08:19 PM -
Basic question about refrigerant to use
By cbfull in forum FundamentalsReplies: 25Last Post: 07-08-2007, 02:19 AM -
Urgent, Kirchoff question
By Peter_1 in forum FundamentalsReplies: 4Last Post: 20-01-2004, 03:12 PM