10-04-2009, 01:59 PM #1
heat load in winter
how to calculate heating load in winter? is it same as calculating cooling load?
-
13-04-2009, 12:54 AM #2
Re: heat load in winter
Not exactly. For example, internal loads are not considered, since it is assumed that the coldest period will be in early morning, possibly unoccupied and at least with no lights, cooking, etc. Second, it is OK, even good practice, to oversize a heating system to allow for morning or Monday warm-up after a set-back period. It is definitely not OK to oversize a cooling system, because that will cause it to run less, hence not dehumidify properly. See ASHRAE Handbook - Fundamentals for commercial and residential heating load calculations. Or ACCA Manual J for residential and ACCA Manual N for commercial. Older versions of the Fundamentals Handbook, such as 1985, are often available on e-bay, and are actually easier to follow than the latest.
-
15-04-2009, 05:43 AM #3
Re: heat load in winter
Theres an argument that you can oversize cooling systems as long as they are inverter controlled. For instance a 3.5kw system. They quote 3.5kw based on the unit being on high fan speed (which can be noisy) you may run the system in low fan speed most of the time so this may actually be providing the required "sizing" of cooling perhaps 2.1kw. With the unit ramping up and down as required.
On days where it gets extra hot you bump up the fan speed and the extra capacity then comes in handy!
Correct me if im wrong!
-
15-04-2009, 11:25 PM #4
-
16-04-2009, 01:22 AM #5
-
16-04-2009, 01:00 PM #6
Re: heat load in winter
If you are considering India as the place so many factors shall change. & you may still end up with heat load which is @ 40 % lower than summer load calculations
-
16-04-2009, 06:08 PM #7
Re: heat load in winter
You are correct. I was discussing heating calculations and didn't expand my statement about cooling systems. Cooling systems should never be designed with excess sensible capacity. At minimum, a cooling system must be designed with sensible heat ratio lower than the room sensible heat ratio. On the other hand, the total capacity of the unit must be equal to or larger than the total room load. One way to match a cooling unit to the load is to operate it at the lowest allowable air flow, usually 300 or 325 cfm/ton. As you point out, this allows an oversized unit to operate with suppressed sensible heat load, and so to dehumidify effectively.
Air flow is generally not adjustable by owner or occupants after a system is installed. As you point out, there are inverter controlled multi-speed air handlers, but airflow changes are controlled by a programmed thermo-humidistat. These units can be specified with some excess sensible capacity to handle maximum db days, and generally reduce air flow when dehumidification is needed.
This is covered more completely in Chapter 7 of my book HVAC Design Manual, A Mechanical Designer's Guide to Successful Design of Small Commercial and Institutional HVAC systems. The book is available for free download by contacting me at my email address.
-
16-04-2009, 06:51 PM #8
Re: heat load in winter
Last edited by back2space; 16-04-2009 at 07:05 PM.
-
17-04-2009, 01:39 AM #9
Re: heat load in winter
I am confused, this topic is 'Heat load in winter" it then went to talk about a 3.5Kw unit.
so when advocating oversizing, is this still in regards to heating and 3.5Kw units?
-
17-04-2009, 02:02 AM #10
Re: heat load in winter
The conversation went onto 3.5kw unit as an example, this could mean any capacity unit. We were reffering to 3.5kw unit in cooling. Oversizing was the main point as units tend to be oversized if sized on cooling. There is always more output on heating.
-
06-05-2009, 11:27 AM #11
Re: heat load in winter
pl tell me how to proceed for calculation of heating load in winter?
-
06-05-2009, 07:44 PM #12
Re: heat load in winter
You could cheat and use this web based heat loss calculator....
http://www.trademate.co.uk/Services/....asp?_brand=CPBrian - Newton Abbot, Devon, UK
Retired March 2015
-
23-05-2009, 11:06 AM #13
Re: heat load in winter
Hi,
I believe heat load in winter is also application dependant.
For commercial applications in indian context winter heat loads are rarely done except for areas where winters have very low temperatures (Few places in india).
What we do is to add reheat Kw in the heat load sheets till SHF works out to 1.00 OR cooling TR becomes Zero (positive) instead of negative which will be the case in winter since heat flows from building to the atmosphere.
For pharma applications where we maintain relative humidity in addition to temperature reheat is calculated such as to maintain required SHF based on inside design conditions. However, during winter we consider inside design conditions to be around 18°C instead of 24°C in order to have lower heating loads.
Thanks
Vijay Kumar Vishwakarma
HVAC EngineerVijay Kumar
HVAC Design Engineer
BMCPL
"The more you sweat in peace less you bleed in war"
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
Heat transfer coefficient - Coolpack
By Graham in forum FundamentalsReplies: 10Last Post: 28-05-2008, 01:08 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM