    Thumbs up Best blend discovered so far
    See the attachment and decide yourself in light of my research paper that R417A(isceon 59) is best low temp refrigerant and direct replacement of R22
    and
    Dudes no oil change is necessary
    Attached Files Attached Files
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
    Oct 2003
    5,630
    Re: Best blend discovered so far
    First time I'm hearing about this.
    Will do some search.
    Good tip Abbasi.
    Peter
    Jun 2001
    N.Ireland
    1,630
    Quote Originally Posted by Peter_1
    Good tip Abbasi.
    Peter
    Peter if this is Isceon 59 it was developed in conjunction with Star Refrigeration, and is being widely used to replace R22 in one of our supermarket chains in the UK.
    Kind Regards. Andy.
    Oct 2003
    5,630
    Andy,
    You're right
    http://www.isceon-refrigerants.co.uk...9-product.html
    Diagrams are the same.
    Will anyway have a closer look at it.
    Have a nice day.
    Peter
    Apr 2004
    Pakistan
    44
    129
    Quote Originally Posted by Andy
    Kind Regards. Andy.
    please can u give me insight as what iwud happen (practically)
    if we use R417A in compressor of R22
    as said no system changes are required how much is this true
    and y dont
    comp manufacurers not mention R417A in catalogues with R407C the former being better 1
    and same price
    Jun 2001
    N.Ireland
    1,630
    Hi abbasi
    the big differance with R407c would be the oil Ester oil is required, but with Isceon 59 no oil changes (apart from normal service changes) is required.
    Kind Regards. Andy.
    St. Louis, MO
    509
    R-417A dew point pressures run below both R-22 and R-407C. At 20°F, R-417A dew point pressure is about 9 psi below R-22 compared to about 5 psi for R-407C. It may become a bit problematic to use a standard R-22 TEV with R-417A as the lower pressures will tend the TEV to overfeed. But R-417A has a lower net refrigerating effect than R-22 which also effectively reduces TEV capacity. As a result, care must be exercised when converting R-22 systems with TEVs to R-417A.
    BTW, the Prof has pondered the Rhodia marketing considerations calling their new line of refrigerant blends the "9 series", i.e., ISCEON 29, 39, 49, 59, 69, 79, 89. What is the significance of the number 9? It is a perfect square. The Hebrews referred to 9 as the symbol of immutable truth. The Ennead is a 9 pointed star, and it once was a sacred symbol...
    The Prof would have opted for the "8 series" however... It would seem much more prosperous. It is the basis of a monetary system. "Pieces of Eight" and "yo ho ho and a bottle of rum". Ok, the Prof has been drinking a wee heavy and needs to rest.
    Prof Sporlan
    Jun 2001
    N.Ireland
    1,630
    Quote Originally Posted by Prof Sporlan
    I would say good sound advise, as with any conversion the expansion device needs checking for correct selection
    Professor you know that the best heavy's are brewed in Ireland and they don't travel well
    I have little experience with Isceon 59 but I know the net refrigeration effect goes down , but the C.O.P goes up. Isceon 69L is the one I have used the most, it is a very good gas, but gives you a lot more refrigerating effect, with an increase in C.O.P, on 69L condensers become too small, design pressures have to be looked at and drive motors can run at their limits but if it's extra capacity you need without chaging the system, on low temperature R69L is the one.
    I suppose one good this with R59 is the fact that more condensing surface becomes available and you never have that problem to consider
    Kind Regards Andy
    5,667
    I've heard that 59 has oil return problems and the oil tends to foam a lot - is this true - has anyone else heard this?
    Only ever used 49 myself as a replacement for R12 in a chill room as we don't tend to work on low temp installations.
  1. Natural Refrigerants
    By baker in forum Refrigerants
    Last Post: 26-10-2010, 05:28 PM
  2. what is the best blend for low temp
    By tony_rich in forum Refrigerants
    Last Post: 05-08-2006, 08:29 AM
  3. Replies: 17
    Last Post: 11-02-2004, 02:23 AM