    Thumbs down McCrap ALS Chiller -Changing Hp setting and getting no help!



    Hi everyone,

    I would like to pick your brains if i may

    Im currently working on two Mcwank ALS chillers, the works involve replacing the P.R.V's on the suction and discharge lines, pressure gauges and new drier cores.

    Great i first thought, until i looked at the Hp cutout on the micro control panel. Its set to 26222kpa which is a little close to the burst point on the P.R.V being 27.6bar!.

    I've read through the previous threads of people asking for the passwords and that but ive had no joy

    I can post up the exact model number when im back on site tomorrow. One last thing, how do you take an oil sample from one of these screw compressors?. It does not have an oil catch tank so that rules that out. Ive tried a plug at the bottom of the compressor but there was next to nothing. Im stuck with my manager breathing done my neck about it.

    Apologies for the rather long post

    Regards

    Matt



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: McCrap ALS Chiller -Changing Hp setting and getting no help!

    Unfortunate name for a peice of equipment.. Quote "Mcwank and McCrap ".
    Respectfully suggest that you stop drinking, walk outside, grab some fresh air and start again, leave all the bull### at home. Then perhaps some one can help you.
    magoo

  3. #3
    Join Date
    Jun 2006
    Location
    england
    Age
    42
    Posts
    25
    Rep Power
    0

    Re: McCrap ALS Chiller -Changing Hp setting and getting no help!

    Hi magoo,

    Thanks for taking the time to read my post. I take on board what you have said regarding the Mcquay and I
    Apologise for it.

    Its just annoying that every other company that builds chillers and or refrigeration
    Plant has a helpfull service desk or helpline. The lady who I spoke to in kent yesterday
    Just didn't want to know unless they looked after the kit.

    Regards

    Matt

  4. #4
    DaikinGuy's Avatar
    DaikinGuy Guest

    Re: McCrap ALS Chiller -Changing Hp setting and getting no help!

    on some frame 4 compressors you have a small valve on the bottom of the external oil seperator. Maybe it might work out to get there a oil sample.

    And 27bar on R134A? Are you sure your fans are running :-)