I've got a walk in cooler at work with two seperate systems. (so feed back is not critical) each system has 2 Evaps (imeco) with TXV's. R-22 is the refrigerant, Copeland Copressor, noticed it not pulling down temp. the compressor is running for a few minutes and its pulling down into a vaccum and trips into an internal overload and restarts. the discharge pressure is staying around 102 psi (which converts on the enthalpy chart to 60 deg. fahrenheit which was what the ambient was at the time. any suggestions
-
21-04-2009, 06:39 AM #2
Re: Copeland Compressor Trouble Shoot
the discharge pressure is to low, R22 has to have around 168 - 196 psi.
its seems to me that you have a lack off *****. or the condensor to cold
greetings
-
21-04-2009, 11:25 PM #3
Re: Copeland Compressor Trouble Shoot
Check for leaks.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-04-2009, 11:45 PM #4
Re: Copeland Compressor Trouble Shoot
This might be due to a loss of refrigerant, or, the head pressure might be too low. I'm betting it is more likely due to leaks if it is pulling into a vacuum.
If all else fails, ask for help.
-
22-04-2009, 12:39 AM #5
Re: Copeland Compressor Trouble Shoot
thanks guys for the input! we've had some problems before with this unit before i got into the refrigeration department i just wanted some verification
Similar Threads
-
Don't shoot me, it's for the beer lovers...
By Brian_UK in forum Chit Chat & Service StoriesReplies: 2Last Post: 06-06-2008, 08:59 PM -
York chiller system trouble shoot
By lawrence7435 in forum Trouble ShootingReplies: 4Last Post: 06-03-2007, 06:54 PM -
How to trouble shoot a system
By US Iceman in forum Trouble ShootingReplies: 12Last Post: 16-02-2007, 08:23 AM -
Don't Shoot the Messenger
By Brian_UK in forum Air ConditioningReplies: 1Last Post: 24-05-2001, 03:17 PM