    Question Copeland Compressor Trouble Shoot



    I've got a walk in cooler at work with two seperate systems. (so feed back is not critical) each system has 2 Evaps (imeco) with TXV's. R-22 is the refrigerant, Copeland Copressor, noticed it not pulling down temp. the compressor is running for a few minutes and its pulling down into a vaccum and trips into an internal overload and restarts. the discharge pressure is staying around 102 psi (which converts on the enthalpy chart to 60 deg. fahrenheit which was what the ambient was at the time. any suggestions



  2. #2
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: Copeland Compressor Trouble Shoot

    the discharge pressure is to low, R22 has to have around 168 - 196 psi.
    its seems to me that you have a lack off *****. or the condensor to cold
    greetings

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Copeland Compressor Trouble Shoot

    Check for leaks.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Copeland Compressor Trouble Shoot

    This might be due to a loss of refrigerant, or, the head pressure might be too low. I'm betting it is more likely due to leaks if it is pulling into a vacuum.
    If all else fails, ask for help.


  5. #5
    Jimmy.Thurman's Avatar
    Jimmy.Thurman Guest

    Re: Copeland Compressor Trouble Shoot

    thanks guys for the input! we've had some problems before with this unit before i got into the refrigeration department i just wanted some verification

Similar Threads

  1. Don't shoot me, it's for the beer lovers...
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 2
    Last Post: 06-06-2008, 08:59 PM
  2. York chiller system trouble shoot
    By lawrence7435 in forum Trouble Shooting
    Replies: 4
    Last Post: 06-03-2007, 06:54 PM
  3. How to trouble shoot a system
    By US Iceman in forum Trouble Shooting
    Replies: 12
    Last Post: 16-02-2007, 08:23 AM
  4. Don't Shoot the Messenger
    By Brian_UK in forum Air Conditioning
    Replies: 1
    Last Post: 24-05-2001, 03:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •