Results 1 to 6 of 6
Thread: Modulating valve
-
13-04-2009, 10:42 PM #1
Modulating valve
I am in search of a 2way modulating valve for chilled glycol coils. Not finding many choices. does anyone know of manufacturers ?
-
13-04-2009, 10:51 PM #2
Re: Modulating valve
Well here's the first one I Googled...
http://dticorp.com/catalog/honeywell...es-p-2239.html
Second...
http://gothermal.thomasnet.com/advan...ves?&forward=1Brian - Newton Abbot, Devon, UK
Retired March 2015
-
13-04-2009, 11:18 PM #3
Re: Modulating valve
Thanks for the reply. I am looking for something more substantial. I am working with coils in the 10 to 25 ton range and I am looking for valve sizes of 1 1/2" on up.
-
13-04-2009, 11:44 PM #4
Re: Modulating valve
OK, understood, I'll see what we can find.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
14-04-2009, 10:06 AM #5
Re: Modulating valve
You could try electrocontrols
http://www.electrocontrols.co.uk/datasheets/V04.pdf
good luckQuidvis Recte Factum Quamvis Humile Praeclarum.
Latine dictum, sit altum videtur.
Si hoc comprehendere potes, gratias age magistro Latinae.
-
21-04-2009, 11:25 PM #6
Re: Modulating valve
Honeywell V5011 series valves with a ML7421 series actuator will give you 0-10 VDC, 2-10 VDC or 4-20 ma control. A simple, yet highly accurate controller would be a Honeywell T775 controller.
Similar Threads
-
Motorized Ball valve versus Globe valve for modulating application
By Sridhar1312 in forum IndustrialReplies: 2Last Post: 06-02-2009, 07:35 PM -
R22 Flooded System - Trawler
By chiefbecker in forum System OptimizationReplies: 18Last Post: 07-02-2008, 11:11 PM -
Service Procedures For TK Scroll
By absolute-zero in forum TransportReplies: 0Last Post: 03-02-2008, 07:42 PM -
Compressor valve test
By RackMechanic in forum Air ConditioningReplies: 11Last Post: 03-02-2008, 05:57 PM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM