Results 1 to 10 of 10
    May 2008
    spain
    54
    63
    Sizing Low temperature rads for Daikin Altherma
    Hi all, i would like some info on the calculation to size low temp rads ( Jaga ) to a Daikin Altherma.
    I am sizing a house at the moment in Spain, i am familiar with heat loss calcs but with flow temperatures of 55 and a return of 45, are the calculations different.
    For example i have a room with a heatloss of 2100watts, now the rads required would be 2 X 1050watts and the physical size of these are 1.2 meters long. But a heating company has given me their calculations based on surface area X 115w psm and their heatloss calc is more or less the same as mine but they have given me 2 X 788watt low temp rads, which is 600 watts short for the room.
    Now i know Low temp rads convect the heat but does that have any bearing on the output of the rad.
    I look forward to any replies.
    Debonair Spain
    Split Croatia
    6,151
    Re: Sizing Low temperature rads for Daikin Altherma
    They should be almost double in size than normal radiators for 75/65°C temperatures.
    So radiators for your system should have catalog power output (75/65°C) of about 2100W to get 1050W at 55/45°C temperatures.
    Why not use fan-coils? They have much better temperature distribution and better suited for low temperature aplication.
    May 2008
    spain
    54
    63
    Hi Nike123 thanks for the quick reply fan coils is not an option because the people prefer central heating.
    I just cannot understand why the heating supplier of the Jaga rads has undersized the whole house.
    I will need to consult further before i submit a price.
    Many thanks
    May 2008
    spain
    54
    63
    Hi all i would appreciate some more comments please.
    Is it too late to fit underfloor heating to take advantage of the lower temperature available?
    edit: Some data relating to the change of radiator sizes is given in this papr....
    http://www.mas.bg.ac.yu/istrazivanje...ac_129-134.pdf
    However, I believe your figures are correct, whatever the radiator is it still needs to output the required design heat loss.
    May 2008
    spain
    54
    63
    Hi Brian thanks for your reply, they were considering underfloor heating and i did suggest that the Altherma would work better with this system
    But as usual money if a factor and it would mean concreting and tiling the whole house, which would put the price up considerably.
    Jul 2008
    London
    848
    When we were all down there, I'm sure the chain smoker said any rads would only need to be 20% bigger...?
    Jul 2008
    London
    848
    Quote Originally Posted by Debonair Spain View Post
    Many thanks
    I know it is Spain but when I had a quote for a new CH system they sized on much lower temps than the Mrs would accept. IE 17 ideg C in the hall bedrooms etc.
    May 2008
    spain
    54
    63
    Hi all yes i believe Multisync could well be right that the Spanish size to 17 degrees c which is not good for the times when you really need it especially when their houses have a tremendous heatloss.
    Thanks for all your help, this site has a wealth of knowledge.
    Nov 2007
    London
    461
    try visiting www.altherma.co.uk
  1. Replies: 12
  2. Superheat and Subcooling
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Last Post: 01-02-2009, 11:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Last Post: 05-12-2007, 06:25 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Last Post: 20-05-2003, 12:27 AM