18-04-2009, 10:57 PM #1
YORK YAES Chiller eprom
i need to adjust the ART timers on the above chiller from 600sec to 300 the chiller serves a critical data centre by the time the timer recycles,a remote high temp alarm has activtaed, can anyone tell me how to do this.
-
18-04-2009, 11:41 PM #2
Re: YORK YAES Chiller eprom
Sound like you have a water capacity problem more than an ART problem.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
19-04-2009, 12:31 AM #3
Re: YORK YAES Chiller eprom
as far as i remember the timer shortens itself dependent on how quickly the water temp is rising, have you a decent sized buffer vessel? are the compressors loading/unloading alright?
al
-
19-04-2009, 06:41 PM #4
Re: YORK YAES Chiller eprom
Welcome Qosmio.
Try speaking to any of your colleagues from the South West Region as they are ALL! Ex York Engineers.
They should be able to Help you?
Grizzly