    a/c in arcade



    Looking to size an arcade for a/c. Was wondering if anyone knew the wattage of poker/fruit/slot machines was, thanks.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: a/c in arcade

    Base it on 230w per machine and you won't go far wrong.

  3. #3
    Join Date
    Feb 2008
    Location
    ireland
    Age
    42
    Posts
    17
    Rep Power
    0

    Re: a/c in arcade

    cheers mate, much appreciated.

  4. #4
    Join Date
    Feb 2008
    Location
    ireland
    Age
    42
    Posts
    17
    Rep Power
    0

    Re: a/c in arcade

    so a 7.1kw for a room 6m x 7.5m x 2.5 with 20 machines and 10 people

    and 12.5kw for a room 9.5mx7.5m.2.5m with 25 machines and 20 people

    that ok.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: a/c in arcade

    I make it 11.5kW and 17.5kW using 125w/m2(rule of thumb)

  6. #6
    Join Date
    Feb 2008
    Location
    ireland
    Age
    42
    Posts
    17
    Rep Power
    0

    Re: a/c in arcade

    ****, don't know how that happened used coolpack too. Again thanks

  7. #7
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: a/c in arcade

    Surely though you have got lighting from those hot halogen spotlights/neon tubes that these machine arcades have.

  8. #8
    Join Date
    Sep 2005
    Location
    South West
    Age
    50
    Posts
    129
    Rep Power
    19

    Re: a/c in arcade

    We recently put a couple of cassettes in an Arcade. We allowed 300w per gaming machine although the client advised us they only use about 150w these days. When using AC Calc to calculate, it worked out about half a KW different to 150w per sq metre rule of thumb.
    Hope this helps.

  9. #9
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: a/c in arcade

    Quote Originally Posted by gwilliamson View Post
    We recently put a couple of cassettes in an Arcade. We allowed 300w per gaming machine although the client advised us they only use about 150w these days. When using AC Calc to calculate, it worked out about half a KW different to 150w per sq metre rule of thumb.
    Hope this helps.
    I do feel it is better to oversize in these situations, for instance, they may put more machines in, they may end up getting very busy and lots of people in the arcade, plus outside ambients may be very high on the off chance that england has a good summer!