10-04-2009, 09:56 AM #1
a/c in arcade
Looking to size an arcade for a/c. Was wondering if anyone knew the wattage of poker/fruit/slot machines was, thanks.
-
11-04-2009, 07:04 PM #2
Re: a/c in arcade
Base it on 230w per machine and you won't go far wrong.
-
11-04-2009, 07:41 PM #3
Re: a/c in arcade
cheers mate, much appreciated.
-
11-04-2009, 08:56 PM #4
Re: a/c in arcade
so a 7.1kw for a room 6m x 7.5m x 2.5 with 20 machines and 10 people
and 12.5kw for a room 9.5mx7.5m.2.5m with 25 machines and 20 people
that ok.
-
11-04-2009, 10:18 PM #5
Re: a/c in arcade
I make it 11.5kW and 17.5kW using 125w/m2(rule of thumb)
-
11-04-2009, 11:11 PM #6
Re: a/c in arcade
****, don't know how that happened used coolpack too. Again thanks
-
13-04-2009, 04:56 PM #7
Re: a/c in arcade
Surely though you have got lighting from those hot halogen spotlights/neon tubes that these machine arcades have.
-
13-04-2009, 05:56 PM #8
Re: a/c in arcade
We recently put a couple of cassettes in an Arcade. We allowed 300w per gaming machine although the client advised us they only use about 150w these days. When using AC Calc to calculate, it worked out about half a KW different to 150w per sq metre rule of thumb.
Hope this helps.
-
15-04-2009, 05:38 AM #9
Re: a/c in arcade