Thread: Heat recovery

  1. #1
    Join Date
    Mar 2008
    Location
    Hereford
    Posts
    39
    Rep Power
    0

    Heat recovery



    Can anyone help?
    I am looking to recover some heat from a large 3 compressor pack by pumping water through a plate heat exchanger fitted inline on the discharge line to the remote condenser and using the warmed up water to suppliment the factory's hot water system.
    If anyone has any useful info regarding this matter I would be very grateful. I have seen systems like this fitted on different sites before, but have never had to install one. Thanks.



  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    17

    Re: Heat recovery

    be careful whit redrawing heat from the compressor(s).if you try to take some heat from the HP line it is possible the condenser will not work properly. if you take heat from the cooling water or compressor itself you will benefit in both ways. the oil in the compressor be cooler,the compression will be higher and so on and on . be careful by changing anything on the line's itself.

    Ice

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Heat recovery

    Desuperheating refrigerant vapor for heat recovery sounds nice and it can provide some heat. However, if the refrigerant vapor has the potential to condense in the desuperheater you can have some problems.

    Most of the desuperheaters I have seen (and their associated refrigerant piping) can provide a way for the condensed vapor to collect in the heat exchanger. If this happens then you loose all heat generation capacity for recovery. This is similar to an air-cooled condenser with head pressure controls that flood the condenser with liquid. It reduced the condenser capacity.

    You have to make sure the liquid refrigerant can drain by gravity to achieve 100% of the rated heat recovery potential.
    If all else fails, ask for help.


  4. #4
    Join Date
    Mar 2008
    Location
    Hereford
    Posts
    39
    Rep Power
    0

    Re: Heat recovery

    Hello US Iceman, thanks for the advice, that makes a lot of sense. So in theory if I install the heat exchanger higher than condenser the condensed vapour should drain into the condenser?
    If so, how does one select the correctly sized heat exchanger? I realize that it does not have to be exact, but I wouldn't want to install a heat exchanger that did nothing at all.
    Also I wouldn't want to install a heat exchanger that was so oversized that it over condensed the refrigerant.
    Any help would be gratefully received.
    Cheers.
    Simon Pyke. UK.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Heat recovery

    Hi Simon.

    The heat recovery exchanger needs to have connections that allow the condensed vapor to drain. I have seen some exchangers which even though single pass on the refrigerant side, they allow the liquid to accumulate.

    The trick is to drain any liquid while allowing the gas to also flow into the condenser.

    I think most of the desuperheater sizing is based on only sensible heat transfer, not latent where condensing occurs.

    You might have to ask the manufacturer and see what he/she says about this, but I think it is all sensible myself.
    If all else fails, ask for help.


  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    51
    Posts
    1,630
    Rep Power
    24

    Re: Heat recovery

    Quote Originally Posted by Pykester1 View Post
    Hello US Iceman, thanks for the advice, that makes a lot of sense. So in theory if I install the heat exchanger higher than condenser the condensed vapour should drain into the condenser?
    If so, how does one select the correctly sized heat exchanger? I realize that it does not have to be exact, but I wouldn't want to install a heat exchanger that did nothing at all.
    Also I wouldn't want to install a heat exchanger that was so oversized that it over condensed the refrigerant.
    Any help would be gratefully received.
    Cheers.
    Simon Pyke. UK.
    Hi Pykester1

    you could size the heat exchanger to 25% of your normal winter THR.

    Kind Regards Andy D
    If you can't fix it leave it that no one else will:rolleyes:

  7. #7
    Join Date
    Dec 2008
    Location
    China
    Posts
    87
    Rep Power
    16

    Re: Heat recovery

    I think a shell and tube heat exchanger can drain the liquid refrigerant quit well coz the refrigerant is in the shell side and we can put it above condenser.

  8. #8
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Heat recovery

    Your condenser outdoors? Your climate such that freezing water with O/D install of concern? Note also: if you employ liquid side regulators for head pressure control, in the cooler season, the air cooled condenser shuts off with liquid refrigerant in it. Depending on Check Valves and etc: This can actually freeze the water in the tubes of an S & T HR even if the S & T is indoors....Regulators need to be on the Discharge Line.

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. Heat recovery and aquifer heat/cold storage
    By RicHoe in forum Supermarket Refrigeration
    Replies: 23
    Last Post: 23-06-2006, 01:24 AM
  5. Heat Recovery for Air Conditioning
    By Student Eng in forum Air Conditioning
    Replies: 5
    Last Post: 13-05-2006, 05:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •