    Faulty ac



    Hi,
    l was working on a carrier split expression unit 2.25hp.The unit works for 15mins and cuts out.The unit doesnt have any safetys like lp or hp.Then the indoor unit light flashes 5 times.l`ve checked the fault codes and it say`s it could be the compressor or low refrigerant.l`ve got my guages connected and the pressures are good. l checked the compressor the windings are good and not down to earth also took the amp draw which is also good.But the compressor is pretty hot,if it is going out on internal overload it wont start back within 5min.l`m thinking it might be the indoor coil sensor which is giving a false reading only 70% sure.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Faulty ac

    Post here your temperature and pressure readings. The "good" doesn't give any value to us.
    In order to properly evaluate the system, we need the air in/air out temps for both coils, the suction line and liquid line temps, and the pressures.
    Also, before measuring, clean your filters and coils, and check for proper air flow!
    Last edited by nike123; 10-03-2009 at 06:45 AM.

  3. #3
    Join Date
    Jan 2009
    Location
    AUSTRALIA
    Posts
    25
    Rep Power
    0

    Re: Faulty ac

    Suction 400kpa Discharge 1410kpa
    Indoor coil supply air 12 degree return air 24 12k split reading.Amp draw for compressor 6.3amps.Filters clean outdoor coil clean.

  4. #4
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: Faulty ac

    hi i dont do too many carriers not sure wat fault code is if it says comp or gas and all checks out id suspect sensor or pcb fault, check for roaches or signs of rats chewin wires i see that a bit id call carrier and find wat causes fault code ie which sensor(s) etc for example if indoor pipe th senses i/d coil below zero it may shut unit down i have a number (02)92024100 you could try good luck with it all

  5. #5
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Faulty ac

    Dear Check, for is there any economy mode is there as the unit behaviour is normal.

  6. #6
    Join Date
    Jan 2009
    Location
    AUSTRALIA
    Posts
    25
    Rep Power
    0

    Re: Faulty ac

    It`s all good now it was the indoor coil sensor thanks

Similar Threads

  1. LG the trail of faulty probes
    By Chris2005 in forum Air Conditioning
    Replies: 17
    Last Post: 15-02-2009, 06:19 PM
  2. Ice Maker (Nice Ice) Faulty: Help!
    By ArthurLeigh in forum Commercial
    Replies: 4
    Last Post: 25-10-2008, 10:49 AM
  3. fujitsu asy faulty
    By julian creamer in forum New to RE
    Replies: 5
    Last Post: 14-08-2008, 11:19 AM
  4. Faulty TXV
    By marc5180 in forum Trouble Shooting
    Replies: 6
    Last Post: 14-06-2007, 11:34 PM
  5. FH4518Y comp faulty
    By Jus Walker in forum Commercial
    Replies: 1
    Last Post: 19-07-2006, 10:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •