    4 doors Freezer cabinet not cold !



    Hello every one , i need some help , any advice would be greatly appreciated .

    I have troubleshooted a 4 doors freezer cabinet 1 1/2 Hp compressor R404A ,cap tube system .Condensing unit on top of the freezer cabinet . Discharge line from compressor go down to the drain pan ( drain pan is under the freezer cabinet and full of water , steam come out from the water ). After that the discharge line from drain pan back to the condenser .Before capillary tube it is a filter drier .

    My client told me that the evaporator very fast block with ice and not cold .I get the data as below ( i use Eliwell digital temperature control to take all the temperature reading and inside the cabinet had no product )
    Evap air in temp : -4°C
    Evap air out temp : -
    Saturated suction temp (SST) :-27°C (17psig)
    Suction line temp at evap outlet : -3°C (wrap with
    insulation )
    Cond air in temp :+29°C
    Cond air out temp :+33°C
    Saturated condensing temp : No service valve
    Liquid line temp at condenser output : +30°C
    Evaporator coil surface : Almost full of ice

    Can i say the system is less of refrigerant because the superheat or Evaporator TD too high ! At the end of troubleshooting , i realized that ,the bottom of the cabinet ( inside the cabinet ) has 2 inches high of water .

    Another question is may i have a similar links that show how to refill refrigerant for cap tube system

    thank you so much !



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 4 doors Freezer cabinet not cold !

    You need to defrost evaporator and then make measurements.
    Charge is done by weight if it is known. If not, than by superheat, but only after you make system performance evaluation.

    http://www.refrigeration-engineer.co...achmentid=2673

    http://www.mediafire.com/?wzgtwmyhzty
    Last edited by nike123; 09-02-2009 at 10:17 AM.

  3. #3
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: 4 doors Freezer cabinet not cold !

    Hello Nike ,thank again for reply.

    The system had stop for few days before i run the compressor and take the readings

  4. #4
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: 4 doors Freezer cabinet not cold !

    I have checked the functioning of digital temperature controller ( 3 signals output model )for the cabinet , It is in good condition . Defrost heating element no problem .

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 4 doors Freezer cabinet not cold !

    What is compressor model# and what is current?

  6. #6
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: 4 doors Freezer cabinet not cold !

    Many thanks Nike . i think i need to go back again.I try to take away those water in the cabinet and run the compressor for second time .

  7. #7
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: 4 doors Freezer cabinet not cold !

    [quote=nike123;134937]What is compressor model# and what is current?

    The compressor model is Tecumseh CAJ2446Z . I forgot to take the reading of compressor running current !

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 4 doors Freezer cabinet not cold !

    Quote Originally Posted by oilzee View Post
    Many thanks Nike . i think i need to go back again.I try to take away those water in the cabinet and run the compressor for second time .
    OK, take also measurement of evaporator air out temperature, and if possible, temperature of one of U turn pipes at middle of condenser. Also, check that evaporator fan is working correctly and that his air flow is OK.

  9. #9
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: 4 doors Freezer cabinet not cold !

    If i use superheat method to evaluate the refrigeration system , suction line temperature at evaporator outlet shouldn't at -3°C when Saturated Suction Temperature (SST)is -27°C. Please correct me if i am wrong .

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 4 doors Freezer cabinet not cold !

    Quote Originally Posted by oilzee View Post
    If i use superheat method to evaluate the refrigeration system , suction line temperature at evaporator outlet shouldn't at -3°C when Saturated Suction Temperature (SST)is -27°C. Please correct me if i am wrong .
    Yes, it should not be-3, but that value depend on evaporator load and air flow at evaporator. So you first need to ensure enough condenser air flow then proper evaporator air flow, then proper load at evaporator, and only then you could evaluate low side and high side pressures and temperatures.

  11. #11
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: 4 doors Freezer cabinet not cold !

    Quote Originally Posted by nike123 View Post
    Yes, it should not be-3, but that value depend on evaporator load and air flow at evaporator. So you first need to ensure enough condenser air flow then proper evaporator air flow, then proper load at evaporator, and only then you could evaluate low side and high side pressures and temperatures.
    OK . i think the evaporator not enough air flow because coil surface almost full of ice .Maybe water inside the cabinet created so much of heat ( when i run the compressor , those water temperature is about +30°C ),due to evaporator absorb a lot of moisture !!

    Evaporator fan motor is in good condition

  12. #12
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: 4 doors Freezer cabinet not cold !

    Dear, First defrost the system and then take the reading as -3 is because of excess frost formation happened.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 4 doors Freezer cabinet not cold !

    If anything, the frozen coil would result in low superheat, but the superheat is in fact high.

    At the same time, the cond dT is low (light load) and the liquid line temp is only slightly above ambient.

    I would be inclined to say that the system is probably short of refrigerant.

    A liquid restriction might give us similar symptoms, but we really can't tell without knowing the subcooling.
    Last edited by Gary; 25-02-2009 at 11:30 AM.

Similar Threads

  1. Cold room/ Freezer combo.
    By dogma in forum Commercial
    Replies: 14
    Last Post: 09-11-2008, 02:25 PM
  2. Hotpoint ffa71 freezer wont go cold
    By efergie in forum Domestic
    Replies: 7
    Last Post: 03-11-2008, 01:44 PM
  3. Hoover Optima - Freezer warm, fridge cold
    By aberchick in forum Domestic
    Replies: 3
    Last Post: 08-05-2008, 09:45 PM
  4. Freezer cabinet problem
    By klimek in forum Technical Discussions
    Replies: 6
    Last Post: 17-03-2008, 11:28 AM
  5. Replies: 11
    Last Post: 16-03-2008, 07:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •