4 doors Freezer cabinet not cold !
Hello every one , i need some help , any advice would be greatly appreciated .
I have troubleshooted a 4 doors freezer cabinet 1 1/2 Hp compressor R404A ,cap tube system .Condensing unit on top of the freezer cabinet . Discharge line from compressor go down to the drain pan ( drain pan is under the freezer cabinet and full of water , steam come out from the water ). After that the discharge line from drain pan back to the condenser .Before capillary tube it is a filter drier .
My client told me that the evaporator very fast block with ice and not cold .I get the data as below ( i use Eliwell digital temperature control to take all the temperature reading and inside the cabinet had no product )
Evap air in temp : -4°C
Evap air out temp : -
Saturated suction temp (SST) :-27°C (17psig)
Suction line temp at evap outlet : -3°C (wrap with
insulation )
Cond air in temp :+29°C
Cond air out temp :+33°C
Saturated condensing temp : No service valve
Liquid line temp at condenser output : +30°C
Evaporator coil surface : Almost full of ice
Can i say the system is less of refrigerant because the superheat or Evaporator TD too high ! At the end of troubleshooting , i realized that ,the bottom of the cabinet ( inside the cabinet ) has 2 inches high of water .
Another question is may i have a similar links that show how to refill refrigerant for cap tube system
thank you so much !
-
09-02-2009, 10:04 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 4 doors Freezer cabinet not cold !
You need to defrost evaporator and then make measurements.
Charge is done by weight if it is known. If not, than by superheat, but only after you make system performance evaluation.
http://www.refrigeration-engineer.co...achmentid=2673
http://www.mediafire.com/?wzgtwmyhztyLast edited by nike123; 09-02-2009 at 10:17 AM.
-
09-02-2009, 10:08 AM #3
Re: 4 doors Freezer cabinet not cold !
Hello Nike ,thank again for reply.
The system had stop for few days before i run the compressor and take the readings
-
09-02-2009, 10:21 AM #4
Re: 4 doors Freezer cabinet not cold !
I have checked the functioning of digital temperature controller ( 3 signals output model )for the cabinet , It is in good condition . Defrost heating element no problem .
-
09-02-2009, 10:36 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 4 doors Freezer cabinet not cold !
What is compressor model# and what is current?
-
09-02-2009, 10:37 AM #6
Re: 4 doors Freezer cabinet not cold !
Many thanks Nike . i think i need to go back again.I try to take away those water in the cabinet and run the compressor for second time .
-
09-02-2009, 10:40 AM #7
Re: 4 doors Freezer cabinet not cold !
[quote=nike123;134937]What is compressor model# and what is current?
The compressor model is Tecumseh CAJ2446Z . I forgot to take the reading of compressor running current !
-
09-02-2009, 10:52 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
09-02-2009, 11:02 AM #9
Re: 4 doors Freezer cabinet not cold !
If i use superheat method to evaluate the refrigeration system , suction line temperature at evaporator outlet shouldn't at -3°C when Saturated Suction Temperature (SST)is -27°C. Please correct me if i am wrong .
-
09-02-2009, 12:23 PM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 4 doors Freezer cabinet not cold !
Yes, it should not be-3, but that value depend on evaporator load and air flow at evaporator. So you first need to ensure enough condenser air flow then proper evaporator air flow, then proper load at evaporator, and only then you could evaluate low side and high side pressures and temperatures.
-
09-02-2009, 12:51 PM #11
Re: 4 doors Freezer cabinet not cold !
OK . i think the evaporator not enough air flow because coil surface almost full of ice .Maybe water inside the cabinet created so much of heat ( when i run the compressor , those water temperature is about +30°C ),due to evaporator absorb a lot of moisture !!
Evaporator fan motor is in good condition
-
25-02-2009, 10:29 AM #12
Re: 4 doors Freezer cabinet not cold !
Dear, First defrost the system and then take the reading as -3 is because of excess frost formation happened.
-
25-02-2009, 11:19 AM #13
Re: 4 doors Freezer cabinet not cold !
If anything, the frozen coil would result in low superheat, but the superheat is in fact high.
At the same time, the cond dT is low (light load) and the liquid line temp is only slightly above ambient.
I would be inclined to say that the system is probably short of refrigerant.
A liquid restriction might give us similar symptoms, but we really can't tell without knowing the subcooling.Last edited by Gary; 25-02-2009 at 11:30 AM.
Similar Threads
-
Cold room/ Freezer combo.
By dogma in forum CommercialReplies: 14Last Post: 09-11-2008, 02:25 PM -
Hotpoint ffa71 freezer wont go cold
By efergie in forum DomesticReplies: 7Last Post: 03-11-2008, 01:44 PM -
Hoover Optima - Freezer warm, fridge cold
By aberchick in forum DomesticReplies: 3Last Post: 08-05-2008, 09:45 PM -
Freezer cabinet problem
By klimek in forum Technical DiscussionsReplies: 6Last Post: 17-03-2008, 11:28 AM -
Beko Fridge Freezer Bubbles & Does Not Get Cold!!!!
By scoobey in forum DomesticReplies: 11Last Post: 16-03-2008, 07:12 PM