    Mitsi VRF actuators



    How is the best way of testing if the actuators for the reversing valves are still working fine? (the little green ones)



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsi VRF actuators

    4 way reversing valves are the same on any heat pump system or VRF system & all operate in the same way.

    On Mitsubishi Electric VRF systems when 240v ac is supplied to the 4w valve coil then the 4w reversing valve changes over to heat mode.
    When 240v ac is turned off to the 4w reversing valve coil then it changes over to cool mode.

    Its very easy with multi meter to see if the 240v ac is being sent from the circuit board to the coil.
    The coil can be tested for correct resistance also with multi meter.
    If its open circuit or closed circuit then it will not operate & if closed circuit will also take out the control circuit fuse on the circuit board.

    Try this basic test.

    Put the system is test heat at the remote controllers.
    when the system has been running for a few mins check to see if the system is heating correctly with correct heating flow of refrigerant.
    Then un plug the 4w reversing valve from the circuit board.
    The 4w reversing valve should change over to cooling mode instantly.
    Then check for correct cooling flow of refrigerant.
    Finally replace the 4w reversing valve plug to the circuit board & now again with 240v ac power to the 4w reversing valve coil it should instantly change back to heating mode.

    This basic test will prove correct operation of the 4w reversing valve.

  3. #3
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Mitsi VRF actuators

    To test the solenoid without a multimeter put unit into heating (or cooling whichever energises the reversing valve) and pass the metal tip of a screwdriver over the top of the solenoid. if the solenoid is energised then the screwdriver will also be attracted to it.
    Also when the plug of an energised reversing valve is pulled off the pcb you should hear a pressure change as the valve changes over
    Brit

  4. #4
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: Mitsi VRF actuators

    two top tips thanks guys

Similar Threads

  1. moving 4 mitsi Elec G50 controllers
    By Enviro-Cooler in forum Air Conditioning
    Replies: 2
    Last Post: 20-01-2009, 08:07 PM
  2. Mitsi Heavy Fault
    By coolments in forum Air Conditioning
    Replies: 2
    Last Post: 22-09-2008, 09:18 AM
  3. Mitsi Electric RP6AA Pump Fault
    By gwilliamson in forum Air Conditioning
    Replies: 8
    Last Post: 15-08-2008, 05:59 PM
  4. Mitsi Lossnay Heat Exchanger
    By sinewave in forum Air Conditioning
    Replies: 9
    Last Post: 05-02-2008, 05:55 PM
  5. Mitsi Problems
    By Latte in forum Air Conditioning
    Replies: 9
    Last Post: 12-02-2005, 07:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •