Re: Cooling down the water in a 1000 liter container
Originally posted by Joep Hogenhout
When I use 1 1000 liter container that water is in about 1 till 2 hour 30\40 degrees celsius when I drive the laser with DC 30A secondary current. The laser needs water with a maximum temperature of 30 degrees celsius, and 8.5 liters/min or 2.2 gal/min
Is there a way to cool the water down to about 10 degrees stable? Please keep in mind that the laser must be able to run the whole night.
So you need a cooler of 1000 x 30 x 1,16 = 34 kW.
MOost positive situation : 1000 l in 2 hour from 15 to 30°C =
1000 *0.5 x 15 x 1.16 = +/- 8 kW.
So your figures should be more precise to calculate your machine.
I should go for this configuration for a Rhoss (relative cheap and good quality, everything build into it, pump, buffer, made to install outside..) of +/- 15 kW.
You can also consider to install 2 independent machines so that you will have a safer setup. If one fails, then you always have the other one as a backup.
You will need +/- 20 to 25 l/kW so 500 l should be sufficient.Last edited by Peter_1; 17-03-2004 at 09:02 PM.
Similar Threads
-
cooling water TDS
By afeef in forum Technical SpeculationsReplies: 1Last Post: 19-04-2009, 07:38 AM -
pure water from air
By Lc_shi in forum New TechnologiesReplies: 32Last Post: 26-02-2009, 12:25 PM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum IndustrialReplies: 5Last Post: 14-10-2005, 06:34 PM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum FundamentalsReplies: 0Last Post: 13-10-2005, 05:14 AM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM