    MSZ GB50VA Requires a 25Amp BS88 Fuse?



    Can some please clarify the following for me: A Mits MSZ GB50VA apparently requires a 25Amp BS88 fuse. I was intending to fit it to a 20AMP MCB, as this appears sufficient to me.
    I called the Mits technical helpline, and was informed that if I don't connect it to a 25AMP BS88 fuse it would void the warranty??? I think this is a nonsense as to how it would void the warranty, but would anyone kindly confirm whether a 20Amp B type MCB would be okay?



  2. #2
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: MSZ GB50VA Requires a 25Amp BS88 Fuse?

    I don't know where the 25A came from.

    Looking at http://www.orionairsales.co.uk/mitsu...rter-233-p.asp

    it says it requires a 16A HRC fuse, so your 20A MCB might be over generous.

    I would try a 16A MCB (B curve) first of all....if you experience tripping you could then try changing to a C curve. Its only got a starting and running current of 5A so I doubt that you should have problems. A lot of these small inverter units will happily run on a 13A spur.

    Don't forget an outside isolator switch.

  3. #3
    Join Date
    Jan 2009
    Location
    england
    Posts
    7
    Rep Power
    0

    Re: MSZ GB50VA Requires a 25Amp BS88 Fuse?

    Thanks for the reply, but the Mits website and tech support say different to your link (i tried pasting the link but it won't let me because i am new to here)
    I will go ahead with the type B 20amp mcb, and thanks again.

  4. #4
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: MSZ GB50VA Requires a 25Amp BS88 Fuse?

    A 20A MCB will be fine for a MSZ-GB50VA.


    We recently installed 5 MSZ-GA71VA where 5 R22 6kW panasonics had been.

    The existing supplies were run in 2.5mm SWA and fused at 16A!

    Just outa curisoty we left them as is and 1 year later there have been no problems with overcurrents.


    Most A/C manufactures way overstate elctrical requirements.


    Your better looking at the min & max amperage draws on the pdf spec sheets.

    He who dies with the most Toys, WINS!

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: MSZ GB50VA Requires a 25Amp BS88 Fuse?

    Remember also that the fuse/mcb is there to protect the cable not the item of equipment at the end of it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jan 2009
    Location
    Ireland
    Posts
    5
    Rep Power
    0

    Re: MSZ GB50VA Requires a 25Amp BS88 Fuse?

    The max running current of the model 50 is 16amp so a 20amp would be the minimum you would fit