    fan cut out on heat



    i have a carrier ac running with r22,
    when on cooling suction is 58psi and machine runs perfectly well all day,
    when on heating the machine runs correctly for approx 10 mins then... fan cuts out, discharge pressure drops from 270 to approx 240 psi and suction drops to approx 35 psi. Obviously the exterior heat exchanger starts to freeze
    i have evacuated system and recharged and i am thinking that my next step would be to link the fan in to run full time in order for external coil to work better.
    Am i missing something obvious?
    is it correct to try linking fan as next step?
    thanks for your assistance in advance



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: fan cut out on heat

    Quote Originally Posted by mangostack View Post
    fan cuts out
    Outdoor fan or indoor fan?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: fan cut out on heat

    Does the fan restart after a period ?

    Should the fan stop as part of the control strategy?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: fan cut out on heat

    Most a/cs have controls that cycle the outdoor fan to stop the indoor coil getting to hot and discharge pressure getting too high.
    If it comes back on, everything is normal. If it cuts out excessively, check pipe work, thermistors, indoor airflow or it may be overcharged (ie precharged to a certain pipe length but installed with a really short run).

    If it doesn't come back on after it first turns off, you have a control problem or even fan motor problem.

    If you wired the outdoor fan to run all the time, your discharge pressure and indoor coil temp would be too high.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: fan cut out on heat

    Check your air filters in indoor unit! Check indoor coil thermistor for proper values against temperature.
    Control logic should not cut-out outdoor fan when pressure is 270 PSI. That is too low pressure/temperature for cut-out. It should be at around 350 PSI (145°F)
    Last edited by nike123; 12-01-2009 at 08:32 AM.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: fan cut out on heat

    Quote Originally Posted by mangostack View Post


    is it correct to try linking fan as next step?
    No, its not! You need to find cause of problem instead of treating symptom.

  7. #7
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: fan cut out on heat

    yeah it sounds like it is not dissipating the heat from the indoor coil, like stated with other responses, indoor coil thermister reading too high, indoor fan motor down on air flow or blocked filters.
    What all the other boys have stated..

  8. #8
    mangostack's Avatar
    mangostack Guest

    Re: fan cut out on heat

    Cheers guys twas the ineterior sensor on pipe, replaced with one that gave a normal reading and all was good

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: fan cut out on heat

    Good, thanks for the update.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. System sizing for heat and manual J
    By Larry2 in forum Heat Pumps
    Replies: 5
    Last Post: 25-06-2008, 10:58 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. heat exchanger for small chiller
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 30-01-2007, 12:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •