11-01-2009, 06:05 PM #1
fan cut out on heat
i have a carrier ac running with r22,
when on cooling suction is 58psi and machine runs perfectly well all day,
when on heating the machine runs correctly for approx 10 mins then... fan cuts out, discharge pressure drops from 270 to approx 240 psi and suction drops to approx 35 psi. Obviously the exterior heat exchanger starts to freeze
i have evacuated system and recharged and i am thinking that my next step would be to link the fan in to run full time in order for external coil to work better.
Am i missing something obvious?
is it correct to try linking fan as next step?
thanks for your assistance in advance
-
11-01-2009, 06:56 PM #2
Re: fan cut out on heat
-
11-01-2009, 11:40 PM #3
Re: fan cut out on heat
Does the fan restart after a period ?
Should the fan stop as part of the control strategy?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-01-2009, 07:28 AM #4
Re: fan cut out on heat
Most a/cs have controls that cycle the outdoor fan to stop the indoor coil getting to hot and discharge pressure getting too high.
If it comes back on, everything is normal. If it cuts out excessively, check pipe work, thermistors, indoor airflow or it may be overcharged (ie precharged to a certain pipe length but installed with a really short run).
If it doesn't come back on after it first turns off, you have a control problem or even fan motor problem.
If you wired the outdoor fan to run all the time, your discharge pressure and indoor coil temp would be too high.
-
12-01-2009, 08:18 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: fan cut out on heat
Check your air filters in indoor unit! Check indoor coil thermistor for proper values against temperature.
Control logic should not cut-out outdoor fan when pressure is 270 PSI. That is too low pressure/temperature for cut-out. It should be at around 350 PSI (145°F)Last edited by nike123; 12-01-2009 at 08:32 AM.
-
12-01-2009, 08:24 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
12-01-2009, 09:34 PM #7
Re: fan cut out on heat
yeah it sounds like it is not dissipating the heat from the indoor coil, like stated with other responses, indoor coil thermister reading too high, indoor fan motor down on air flow or blocked filters.
What all the other boys have stated..
-
18-01-2009, 04:03 PM #8
Re: fan cut out on heat
Cheers guys twas the ineterior sensor on pipe, replaced with one that gave a normal reading and all was good
-
18-01-2009, 04:35 PM #9
Re: fan cut out on heat
Good, thanks for the update.
Brian - Newton Abbot, Devon, UK
Retired March 2015
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
System sizing for heat and manual J
By Larry2 in forum Heat PumpsReplies: 5Last Post: 25-06-2008, 10:58 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
heat exchanger for small chiller
By star882 in forum FundamentalsReplies: 4Last Post: 30-01-2007, 12:06 PM