Thread: Help with mitsi
-
11-01-2009, 10:30 PM #1
Help with mitsi
hey ive got a mitsi condenser pury-p250ygm-a and 5 indoors plfy p63vame. the original set up was 2 of the units had being in a office and now they have split them up. i went and added a additional remote control to the unit in the new office and wired it correctly and addressed the remote. all was working fine and dandy untill i got a call out to the client the units will not controll individually. i can only run both units when the new remote is turned on, any ideas ?
-
11-01-2009, 11:23 PM #2
Re: Help with mitsi
Double/triple check all of the unit addresses, system settings and wiring connections.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-01-2009, 11:23 PM #3
Re: Help with mitsi
This is not daikin system
Just because you connected the remote control to the indoor unit & set address it will not control only that indoor unit
&
other remote controls which were set to contol a group of indoor units will not change to individual contol unless you change address & group control settings
Please advise address settings for all units & remote controllers & also which units need to have individual control & which units need group control
first you need to understand basic mitsubishi address setting logic
then
you can make new address settings which will work
then
you can set correct address settings & carry out virgin restart
then all unit will work as you require
Similar Threads
-
Mitsi Heavy Fault
By coolments in forum Air ConditioningReplies: 2Last Post: 22-09-2008, 09:18 AM -
Mitsi Electric RP6AA Pump Fault
By gwilliamson in forum Air ConditioningReplies: 8Last Post: 15-08-2008, 05:59 PM -
Mitsi Lossnay Heat Exchanger
By sinewave in forum Air ConditioningReplies: 9Last Post: 05-02-2008, 05:55 PM -
mitsi r22 to 410a system
By rbartlett in forum Air ConditioningReplies: 3Last Post: 28-08-2006, 08:36 PM -
Mitsi Problems
By Latte in forum Air ConditioningReplies: 9Last Post: 12-02-2005, 07:22 PM