04-12-2008, 05:05 PM #1
Noise problem on DAIKIN 4MXS68F2
Hi everyone
I have a strange and boring problem on an installation consisting of:
1x 4MXS68F2V daikin outdoor unit
3x FTXS20G2 for 3 bedrooms
1x FTXS25G2 for the dinning room
We have an abnormal noise inside the copper pipes -just like a water flow- while running in heating mode.
The dinning room's piping are passing inside a bedroom through a thermoplastic profile (i don't what's the english for exactly, see the attachment and give the word in english please...).
We hear the noise when the bedroom's unit is thermostat OFF (fan OFF also) and the dinning room's unit thermostat ON.
Any idea well-appreciated
rgds
cool#9
-
05-12-2008, 12:00 AM #2
Re: Noise problem on DAIKIN 4MXS68F2
For 'profile' read 'trunking' or 'conduit'.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
05-12-2008, 10:58 AM #3
Re: Noise problem on DAIKIN 4MXS68F2
it is normal for all units to have gas circulating through the pipes when in heating even if some are thermostat off. The txv valves outside unit remain partially open on units that are off to facilitate oil return to the compressor. There is nothing you can do to stop this happening. If the unit is not workin properly then call an engineer otherwise try to maybe insulate the pipes better to provide noise reduction.
-
03-01-2009, 02:43 PM #4
Re: Noise problem on DAIKIN 4MXS68F2
In relation to this unit, have you chopped off the muffler on the liquid line? some people cut and braze instead of flaring and chop off the muffler, this will make the indoor units noisy, if this has been done you can order a new mufler and fit it, keeping in mind that some indoor units have 2 mufflers.
Also check the total length of pipework installed to see if you have enough refrigerant charge in the system.
If all of this is ok, it is the refrigerant passing through the indoor fan coil, but this is mainly on VRV systems that the EXV will stay partially open to give a minimum coil surface area as the condensing unit coil surface is sized much larger for cooling.
Similar Threads
-
daikin L0 inverter problem
By robin r33 gtr in forum Air ConditioningReplies: 17Last Post: 11-03-2010, 11:25 PM -
daikin G, B series problem
By yanatahyana in forum Air ConditioningReplies: 9Last Post: 22-08-2008, 04:51 AM -
Daikin split problem (any ideas)
By airconjohn in forum Air ConditioningReplies: 14Last Post: 17-02-2008, 08:40 PM -
!!big Daikin Problem!! Codes,u4,pj, And E0
By airconengineer in forum Air ConditioningReplies: 21Last Post: 31-05-2007, 09:04 PM -
Daikin problem
By Jambo in forum Trouble ShootingReplies: 4Last Post: 28-07-2006, 07:42 PM