    Noise problem on DAIKIN 4MXS68F2



    Hi everyone
    I have a strange and boring problem on an installation consisting of:
    1x 4MXS68F2V daikin outdoor unit
    3x FTXS20G2 for 3 bedrooms
    1x FTXS25G2 for the dinning room
    We have an abnormal noise inside the copper pipes -just like a water flow- while running in heating mode.
    The dinning room's piping are passing inside a bedroom through a thermoplastic profile (i don't what's the english for exactly, see the attachment and give the word in english please...).
    We hear the noise when the bedroom's unit is thermostat OFF (fan OFF also) and the dinning room's unit thermostat ON.
    Any idea well-appreciated
    rgds
    cool#9
    Attached Images Attached Images



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Noise problem on DAIKIN 4MXS68F2

    For 'profile' read 'trunking' or 'conduit'.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Noise problem on DAIKIN 4MXS68F2

    it is normal for all units to have gas circulating through the pipes when in heating even if some are thermostat off. The txv valves outside unit remain partially open on units that are off to facilitate oil return to the compressor. There is nothing you can do to stop this happening. If the unit is not workin properly then call an engineer otherwise try to maybe insulate the pipes better to provide noise reduction.

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Noise problem on DAIKIN 4MXS68F2

    In relation to this unit, have you chopped off the muffler on the liquid line? some people cut and braze instead of flaring and chop off the muffler, this will make the indoor units noisy, if this has been done you can order a new mufler and fit it, keeping in mind that some indoor units have 2 mufflers.

    Also check the total length of pipework installed to see if you have enough refrigerant charge in the system.
    If all of this is ok, it is the refrigerant passing through the indoor fan coil, but this is mainly on VRV systems that the EXV will stay partially open to give a minimum coil surface area as the condensing unit coil surface is sized much larger for cooling.

Similar Threads

  1. daikin L0 inverter problem
    By robin r33 gtr in forum Air Conditioning
    Replies: 17
    Last Post: 11-03-2010, 11:25 PM
  2. daikin G, B series problem
    By yanatahyana in forum Air Conditioning
    Replies: 9
    Last Post: 22-08-2008, 04:51 AM
  3. Daikin split problem (any ideas)
    By airconjohn in forum Air Conditioning
    Replies: 14
    Last Post: 17-02-2008, 08:40 PM
  4. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  5. Daikin problem
    By Jambo in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2006, 07:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •