Re: LG heat pump problem
And that is exactly how it should behave according to control strategy, and if the dip switch mean that air return sensor is offset by 4K.
Thermatech, thanks for your comments, but how to tell if the system has a fault.
One thing I can advise you is if I set the remote controller to 30C the outdoor unit current drawn is about 500watts higher than if it was maintaining the setpoint. I have just tried this now. So the compressor is not running 100% but it doesnt ramp down any more.
If change in one capacity step is enough to maintain set temperature within 1K than there is no need to ramp down any more. Only if that capacity change doesn't establish 1K temperature control, outdoor unit switch to lower capacity step and etc...
Please, read that text above carefully few times because, that is foundation for understanding of function of control logic. And, it seems, that part is most confusing to you, according to your questions.
P.S. Sorry, if I something misunderstood, because of language.Last edited by nike123; 27-12-2008 at 12:25 PM.
Similar Threads
-
Design heat pump for a pool
By rolandh in forum Heat PumpsReplies: 10Last Post: 23-09-2010, 10:50 AM -
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Heat Pump components
By mayo in forum Heat PumpsReplies: 22Last Post: 04-05-2009, 07:29 AM -
Heat pump problem
By Darc in forum Trouble ShootingReplies: 5Last Post: 23-08-2008, 10:21 AM -
bath room reclaim heat pump
By Lc_shi in forum Heat PumpsReplies: 2Last Post: 19-11-2007, 08:59 PM