    york underceiling



    hie guys any help

    the york air con model # moh45n36bof 48 000 btu/h.the compressor is running for 44 sec in both cooling and heating.refrigerant charge is ok.but the control circuit relay is switching off during this time.it repeats after 3 min. any help urgent guys.water pump always on.

    bright



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: york underceiling

    Quote Originally Posted by bright View Post
    hie guys any help

    the york air con model # moh45n36bof 48 000 btu/h.the compressor is running for 44 sec in both cooling and heating.refrigerant charge is ok.but the control circuit relay is switching off during this time.it repeats after 3 min. any help urgent guys.water pump always on.

    bright
    have you checked all safety switch's

    LP
    HP
    water flow switch

    is the BMS signal ok? will it run in hand mode?
    Paul


    "KEEP IT COOL"

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. YORK ducted split
    By ALONEI in forum Trouble Shooting
    Replies: 7
    Last Post: 10-07-2010, 02:18 AM
  3. York Wiring Diagrams
    By iceman007 in forum Trouble Shooting
    Replies: 14
    Last Post: 10-04-2010, 06:48 PM
  4. York Lch Series Schematics
    By greg56 in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 04-08-2008, 02:31 AM
  5. York Controller Password
    By marc5180 in forum Air Conditioning
    Replies: 6
    Last Post: 29-02-2008, 06:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •