    Bitzer help



    hi all,
    i have problems on a 12hp coolroom system. The system was running with less than half its evaporators (coroded away!) and missing the high condensing fan for who knows how long. A while ago the "black box" temperature cutout was out and we assumed the cond. fan problem. Fixed that but motor current way to high (using 11kw instead of 8!) and evaporating way to low.
    Replaced evaps, current back down to normal levels, but now the compressor is making a knocking sound.
    On top of this the compressor has never (10yrs old) had an oil change!
    Can people help with a plan of attack? gas change (r409a at momnet)? oil?
    thanks in advance.



  2. #2
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Bitzer help

    Clanking or banging compressor noises, at least the costly ones, are usually due to a loose connecting rod, piston pin, crankshaft, or other internal part. The compressor noise could also be due to refrigerant liquid "floodback" into the compressor crankcase. If this is the problem the noise will appear only at the interval of compressor start-up also a low oil condition in the compressor unit. You might want to pump it down to about 16 “ and see if it holds to ck the suction and discharge valves

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bitzer help

    First things first!
    Knocking sound indicates possible liquid flood back. Check evaporator and total superheat while compressor is still alive !
    Last edited by nike123; 14-12-2008 at 09:58 AM.

  4. #4
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: Bitzer help

    super heat is 10k (when the room is at 8 deg) at both the evaporators and picks up another 3 k to the condensing unit. bulbs are properly insulated and attached 45deg to bottom.
    what is the result of liquid slugging in this type of compressor?
    thank you.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bitzer help

    Quote Originally Posted by Harrison View Post
    super heat is 10k (when the room is at 8 deg) at both the evaporators and picks up another 3 k to the condensing unit. bulbs are properly insulated and attached 45deg to bottom.
    what is the result of liquid slugging in this type of compressor?
    thank you.
    Result is something broken.

  6. #6
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: Bitzer help

    something broken!! what, are you telling me you cant compress a liquid. so what would break?

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer help

    Quote Originally Posted by Harrison View Post
    something broken!! what, are you telling me you cant compress a liquid. so what would break?
    You can never compress a liquid, that's since the beginning of earth.
    Pistons, rod, and in worst case several pistons, pieces of iron will explode in the windings and on top of that, you will have a burnt motor.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: Bitzer help

    i was joking peter 1 but seriously, in practice liquid slugging causes such severe mechanical damage? i was thinking that a bit of liquid back would damage valves perhaps, but large quantities would obviously cause the said mech carnage!

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer help

    I have others, pistons are twisted in their housings
    Attached Images Attached Images
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bitzer help

    Quote Originally Posted by Harrison View Post
    something broken!! what, are you telling me you cant compress a liquid. so what would break?
    If you click to "broken" in my response you will find what.

    Here is another link!

    Did you checked if oil level is to high? Do you have excessive oil foaming?
    That also could be cause of knocking sound!

    Bitzers are rugged and may tolerate small amount of liquid hammering (oil or refrigerant) for short periods.

Similar Threads

  1. Bitzer gasket
    By Renato RR in forum Fundamentals
    Replies: 5
    Last Post: 04-11-2010, 10:08 AM
  2. Bitzer s6f30 2-stage compressors
    By JONAH in forum Technical Discussions
    Replies: 25
    Last Post: 27-10-2010, 07:27 AM
  3. Bitzer CSH8561-125Y oil sight glass
    By Peter_1 in forum Industrial
    Replies: 40
    Last Post: 26-05-2010, 04:32 PM
  4. Rewiding Stator Bitzer Hskc 7461-80
    By nanev in forum Electrical
    Replies: 1
    Last Post: 01-09-2008, 07:32 PM
  5. Commissioning Bitzer Screws
    By Andy in forum Commissioning
    Replies: 6
    Last Post: 22-11-2006, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •