13-12-2008, 10:00 PM #1
Bitzer help
hi all,
i have problems on a 12hp coolroom system. The system was running with less than half its evaporators (coroded away!) and missing the high condensing fan for who knows how long. A while ago the "black box" temperature cutout was out and we assumed the cond. fan problem. Fixed that but motor current way to high (using 11kw instead of 8!) and evaporating way to low.
Replaced evaps, current back down to normal levels, but now the compressor is making a knocking sound.
On top of this the compressor has never (10yrs old) had an oil change!
Can people help with a plan of attack? gas change (r409a at momnet)? oil?
thanks in advance.
-
14-12-2008, 12:58 AM #2
Re: Bitzer help
Clanking or banging compressor noises, at least the costly ones, are usually due to a loose connecting rod, piston pin, crankshaft, or other internal part. The compressor noise could also be due to refrigerant liquid "floodback" into the compressor crankcase. If this is the problem the noise will appear only at the interval of compressor start-up also a low oil condition in the compressor unit. You might want to pump it down to about 16 “ and see if it holds to ck the suction and discharge valves
-
14-12-2008, 12:59 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Bitzer help
First things first!
Knocking sound indicates possible liquid flood back. Check evaporator and total superheat while compressor is still alive !Last edited by nike123; 14-12-2008 at 09:58 AM.
-
14-12-2008, 07:45 AM #4
Re: Bitzer help
super heat is 10k (when the room is at 8 deg) at both the evaporators and picks up another 3 k to the condensing unit. bulbs are properly insulated and attached 45deg to bottom.
what is the result of liquid slugging in this type of compressor?
thank you.
-
14-12-2008, 08:30 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Bitzer help
Result is something broken.
-
14-12-2008, 09:07 AM #6
Re: Bitzer help
something broken!! what, are you telling me you cant compress a liquid
. so what would break?
-
14-12-2008, 09:46 AM #7
Re: Bitzer help
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-12-2008, 10:16 AM #8
Re: Bitzer help
i was joking peter 1
but seriously, in practice liquid slugging causes such severe mechanical damage? i was thinking that a bit of liquid back would damage valves perhaps, but large quantities would obviously cause the said mech carnage!
-
14-12-2008, 11:05 AM #9
Re: Bitzer help
I have others, pistons are twisted in their housings
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-12-2008, 11:08 AM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Bitzer help
If you click to "broken" in my response you will find what.
Here is another link!
Did you checked if oil level is to high? Do you have excessive oil foaming?
That also could be cause of knocking sound!
Bitzers are rugged and may tolerate small amount of liquid hammering (oil or refrigerant) for short periods.
Similar Threads
-
Bitzer gasket
By Renato RR in forum FundamentalsReplies: 5Last Post: 04-11-2010, 10:08 AM -
Bitzer s6f30 2-stage compressors
By JONAH in forum Technical DiscussionsReplies: 25Last Post: 27-10-2010, 07:27 AM -
Bitzer CSH8561-125Y oil sight glass
By Peter_1 in forum IndustrialReplies: 40Last Post: 26-05-2010, 04:32 PM -
Rewiding Stator Bitzer Hskc 7461-80
By nanev in forum ElectricalReplies: 1Last Post: 01-09-2008, 07:32 PM -
Commissioning Bitzer Screws
By Andy in forum CommissioningReplies: 6Last Post: 22-11-2006, 09:12 AM