    Question Mitsubishi VRF problems



    Hi Guys,
    Maybe someone can help me...I have two systems.Each one is
    27 fan coils
    BC master 16 way
    BC slave 16 way
    PURY P500 YHM
    After I've done the gas charge I got a problem with the last five coils from the master BC. It won't work neither cooling or heating.I' m sure the gas charge is wright,because I double check.When they are runing on their own,are working fine.With the dip switches from the outdoor I forced them to finish the initial mode.In the test run , same symptoms.I unpluged the LEV's from the BC board trying to reset them, but no changes.I know it sounds like short gas but I don't want to overcharge those systems.Strange thing is happening because the two systems have the same symptomps.Discharge and suction pressure are looking good interogating the outdoor.Also, temperature on the suction and discharge are good.
    Many Thanks.



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi VRF problems

    Please can you confirm the following.

    1/ the outdoor unit has been running for more than 1 hr with 3ph power on & has therefore commpleted initial run time ?

    2/ Then what happens when you test run the five indoor units with everything else off ?

    3/ What is the total capacity of all the indoor units added up ?

    4/ Is 240v power on to the circuit board on the 5 indoor units ?

    5/ Is the branch address set at each indoor unit correct fro the refrigeration pipe connections at the B/C ports ?

  3. #3
    aircon4you1's Avatar
    aircon4you1 Guest

    Re: Mitsubishi VRF problems

    I sorted out,it was just the initial mode longer then normal...Many thanks.

  4. #4
    SAW MYO HLAING's Avatar
    SAW MYO HLAING Guest

    Re: Mitsubishi VRF problems

    Hello, I am SAW MYO HLAING, a new member, would like to know about Carrier VRV System and troubleshooting.
    Thanks
    Saw
    sawmyohlaing@gmail.com

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Mitsubishi VRF problems

    Quote Originally Posted by SAW MYO HLAING View Post
    Hello, I am SAW MYO HLAING, a new member, would like to know about Carrier VRV System and troubleshooting.
    Thanks
    Saw
    sawmyohlaing@gmail.com

    Hi SAW MYO HLAING! Welcome to RE!
    You are not replaying to this thread, so, please, post your own question here!
    Last edited by nike123; 11-12-2008 at 04:16 PM.

Similar Threads

  1. Mitsubishi City multi problems
    By cooltech1 in forum Air Conditioning
    Replies: 9
    Last Post: 24-01-2010, 06:03 PM
  2. mitsubishi vrf problem!
    By airconadam in forum Air Conditioning
    Replies: 16
    Last Post: 08-11-2008, 06:50 PM
  3. Mitsubishi problems
    By Swedish AC in forum Air Conditioning
    Replies: 12
    Last Post: 14-05-2008, 11:38 AM
  4. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •