    what are the specifications of the evaporator and condenser that i need?



    hi
    I'm building a small air condition to a very small room.
    The compressor cooling capacity is 350 watt
    1-What are the technical specifications of the evaporator coil that i need?
    2- What are the technical specifications of the condenser coil that i need?
    Thank you
    Last edited by Brian_UK; 06-12-2008 at 10:54 PM.



  2. #2
    toro's Avatar
    toro Guest

    Re: what are the specifications of the evaporator and condenser that i need?

    the compressor is GD30MB

    electrolux


  3. #3
    Join Date
    Nov 2006
    Location
    Kolkata, West Bengal, India
    Age
    64
    Posts
    10
    Rep Power
    0

    Re: what are the specifications of the evaporator and condenser that i need?

    Your heat load appers to be wrong. Please re-calculate the load. If the load is correct it is not a problem to design the evaporator and condenser.