hi
I'm building a small air condition to a very small room.
The compressor cooling capacity is 350 watt
1-What are the technical specifications of the evaporator coil that i need?
2- What are the technical specifications of the condenser coil that i need?
Thank youLast edited by Brian_UK; 06-12-2008 at 10:54 PM.
-
06-12-2008, 10:49 PM #2
Re: what are the specifications of the evaporator and condenser that i need?
the compressor is GD30MB
electrolux
-
10-12-2008, 09:39 AM #3
Re: what are the specifications of the evaporator and condenser that i need?
Your heat load appers to be wrong. Please re-calculate the load. If the load is correct it is not a problem to design the evaporator and condenser.