09-12-2008, 02:40 PM #2
Re: Markus heat pump problem
It may be low on gas or have a defect expansion valve. In addition the manufacturer installed a to small expansion valve on some R134A pumps causing unnecessarily low evaporating temperature. I suppose your pump has no liquid sight glass. If it dont have one, then the proper procedure is to measure the high pressure, convert it to temperature, measure the condenser refrigerant outlet temperature and fill the system until the pressure derived temperature gets roughly 3 to 4C warmer than the condenser outlet refrigerant temperature.
As you now have tampered with the expansion valve adjustment you have to observe the suction superheat as you fill the system and adjust the expansion valve as required.
If the pressure derived temperature already is warmer, then your expansion valve probably is defect.