Results 1 to 6 of 6
  1. #1
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Which chilling system?



    I am involved with building of new hatchery,

    They will need about 100 TR water chiller for cooling the hatching cells and Ac.

    I am thinking of manufacture the chiller myself.

    There are a few cooling methods:

    Falling film chiller
    Shel & tube
    Plate heat exchanger
    Ice builder

    what would you prefer and why?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Which chilling system?

    Plate & frame (or brazed plates) to limit refrigerant charge.

    An ice builder if you have On-Peak & Off-Peak electrical rates.
    If all else fails, ask for help.


  3. #3
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Which chilling system?

    prefer plate heat exchanger if water average temp is 33 to 36 fahrenheit.we have done this before on poultry proccessing.

    regards
    abet

  4. #4
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: Which chilling system?

    B"H
    Hello Chemi,
    No enough information:
    type of water (sea or fresh?)
    tem-re range
    if the cleaning of the surface is needed

  5. #5
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: Which chilling system?

    B"H
    I would agree with US Iceman

  6. #6
    baskaran's Avatar
    baskaran Guest

    Re: Which chilling system?

    water chilling for chicken cutting section they used,the water temperature req is 5 deg , this one is closed system during night time the chiller got freezed, the running pressure is 4.5bar, what temp and pressure the chiller got freezed?

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  4. Replies: 19
    Last Post: 15-04-2008, 07:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •