    Air conditioning energy consumption



    Hi all,

    I'm currently working on the development of a new hybrid ventilation system that has the ability to warm and cool incoming supply air.

    Now we want to compare the energy use of the system with that of a 'through the wall' packaged air conditioner. We're using CIBSE weather data that gives an hour-by-hour account of a typical year. I've worked out how much energy our system will use, but am struggling to find any data on how much energy an equivalent a/c system would consume.

    Any ideas?

    Thanks in advance!



  2. #2
    Join Date
    Feb 2006
    Location
    Mumbai
    Posts
    49
    Rep Power
    0

    Re: Air conditioning energy consumption

    Hi,

    Can details be provided on method by which air is being cooled / warmed.

    Regards
    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  3. #3
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Our system simply circulates hot or cold water through a heat exchanging copper coil. The air passes over the coil and then into the room.

    We 'd like to compare to a compressor-based refrigerant system of around 1kW.

  4. #4
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    A bit more detail:

    Over the period of one year our unit will use 57kWh to maintain a supply air temperature of 20C at 40l/s over the summer (i.e. when ambient temperature is above 20C).

    Over the winter the unit will require 780kWh to supply air at 18C, again at 40l/s whenever ambient temperature drops below 18C.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning energy consumption

    Energy consumption can be compared only by comparing COP for different weather conditions of your system and given "window shaker".

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Air conditioning energy consumption

    I think you should also be aware that you are trying to compare two completely different systems.

    You are designing a ventilation system
    but you are doing a cost comparison with an air recirculation system.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by Brian_UK View Post
    I think you should also be aware that you are trying to compare two completely different systems.

    You are designing a ventilation system
    but you are doing a cost comparison with an air recirculation system.
    Yes I realised this! My problem is that I work under two supervisors- an academic supervisor who told me that you can't compare the two systems, and an industry supervisor who wants me to compare them nevertheless!

    Some might say that I'm stuck between a rock and a hard place.

  8. #8
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Any idea how converting a through the wall air conditioner to use fresh air would affect the COP? I think what I'm being asked to do is not possible

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    Any idea how converting a through the wall air conditioner to use fresh air would affect the COP? I think what I'm being asked to do is not possible
    Fresh air doesn't affect COP of unit but gives additional heat load to the conditioned space!

    Many window shakers have flap to introduce 5-10% fresh air of their circulation rate!

  10. #10
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by nike123 View Post
    Fresh air doesn't affect COP of unit but gives additional heat load to the conditioned space!

    Many window shakers have flap to introduce 5-10% fresh air of their circulation rate!
    Ok I understand. So I need to work out the extra heat load generated by 100% fresh air. Which is obviously dependent on outside air temperature.

    Any idea where I can find typical COPs for these window shakers? Manufacturer's literature is extremely vague!

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    Ok I understand. So I need to work out the extra heat load generated by 100% fresh air.
    Why 100%?

    Any idea where I can find typical COPs for these window shakers? Manufacturer's literature is extremely vague!
    It is usually between 2.5 and 3.5!

    Maybe Eurovent site.
    I am sure that you could always send e-mail to manufacturer for that data!

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    A bit more detail:

    Over the period of one year our unit will use 57kWh to maintain a supply air temperature of 20C at 40l/s over the summer (i.e. when ambient temperature is above 20C).
    Are you saying you want the temperature of the room air to be 20C?... or the temperature of the air leaving the coil to be 20C?

  13. #13
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by Gary View Post
    Are you saying you want the temperature of the room air to be 20C?... or the temperature of the air leaving the coil to be 20C?
    Temperature of the air leaving the coil to be 20C...

  14. #14
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by nike123 View Post
    Why 100%?



    It is usually between 2.5 and 3.5!

    Maybe Eurovent site.
    I am sure that you could always send e-mail to manufacturer for that data!
    I'm looking at a ventilation unit that uses 100% fresh air, and then trying to compare it to a different sort of unit to see if it offers any advantages from an energy point of view.

    Basically trying to find a way to justify the development of the new unit. Which is quite hard!

    edit: That eurovent site is brilliant- thanks!
    Last edited by wilsonudevil; 13-11-2008 at 03:08 PM.

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    Temperature of the air leaving the coil to be 20C...
    A 20C coil is going to remove little if any moisture from the fresh air. You are going to have a very humid room.

    For example, if you take 30C fresh air at 50%RH and cool it to 20C, its RH will be 90%.
    Last edited by Gary; 13-11-2008 at 03:21 PM.

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    I'm looking at a ventilation unit that uses 100% fresh air, and then trying to compare it to a different sort of unit to see if it offers any advantages from an energy point of view.
    Ventilation unit doesn't cools or heat air, and therefore, cannot be compared with air-conditioning unit!
    Or you using wrong terms here?

  17. #17
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Air conditioning energy consumption

    @ Nike He is stuck between a hard spot as usual industry guy wants to compare two non comparable items!

    I feel for the poor guy!

  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    Our system simply circulates hot or cold water through a heat exchanging copper coil. The air passes over the coil and then into the room.
    How are you heating/cooling the water?

  19. #19
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by nike123 View Post
    Ventilation unit doesn't cools or heat air, and therefore, cannot be compared with air-conditioning unit!
    Or you using wrong terms here?
    This particular ventilation unit has the ability to temper the air. So during the winter it warms the ventilation air and during the summer it cools it.

    I agree it can't be compared with a conventional air conditioning unit that's primary function is to cool the ambient room air!

  20. #20
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by Gary View Post
    How are you heating/cooling the water?
    The air is being warmed/cooled using a finned tube heat exchanger with warm/cool water circulating inside it.

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    The air is being warmed/cooled using a finned tube heat exchanger with warm/cool water circulating inside it.
    And that water is being heated/cooled by ______?

  22. #22
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by Gary View Post
    And that water is being heated/cooled by ______?
    Cooling/heating the water with one of those combined electric water heater/chillers. Basically a recirculating bath with a heating/cooling element.

  23. #23
    Join Date
    Aug 2008
    Location
    Reading
    Posts
    26
    Rep Power
    0

    Re: Air conditioning energy consumption

    Quote Originally Posted by Gary View Post
    A 20C coil is going to remove little if any moisture from the fresh air. You are going to have a very humid room.

    For example, if you take 30C fresh air at 50%RH and cool it to 20C, its RH will be 90%.
    I've always wondered about that (well, since I got into the whole thermal comfort/indoor air field). When you cool air it becomes more humid. But the actual water content of the air remains the same. So why does it feel 'wetter' since there isn't actually any more water in the air?

  24. #24
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Air conditioning energy consumption


  25. #25
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    Cooling/heating the water with one of those combined electric water heater/chillers. Basically a recirculating bath with a heating/cooling element.
    Therein lies your energy usage... and your basis for comparison.

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Air conditioning energy consumption

    Quote Originally Posted by wilsonudevil View Post
    I've always wondered about that (well, since I got into the whole thermal comfort/indoor air field). When you cool air it becomes more humid. But the actual water content of the air remains the same. So why does it feel 'wetter' since there isn't actually any more water in the air?
    A major part of your body's cooling mechanism is the evaporation of moisture from your skin.

    Less humid air is more absorbent and helps this process. In very dry climates the moisture evaporates so fast you may not even realize you are sweating.

    More humid air is less absorbent and hinders this process, making you feel wetter because you are wetter.

Similar Threads

  1. Ambient temperature and fridge energy consumption
    By elita in forum Fundamentals
    Replies: 1
    Last Post: 08-12-2007, 12:32 PM
  2. Very High Energy Consumption
    By gdiaz in forum Trouble Shooting
    Replies: 12
    Last Post: 17-01-2007, 03:56 PM
  3. need energy consumption data
    By gokhan in forum Technical Discussions
    Replies: 2
    Last Post: 25-05-2006, 12:48 AM
  4. Direct Energy Consumption Question
    By v8dve in forum Fundamentals
    Replies: 1
    Last Post: 05-04-2003, 03:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •