Thread: Daikin Inverter error code F3
-
16-11-2008, 06:57 AM #1
Daikin Inverter error code F3
Hi, i've been having problems with my Daikin inverter also. Its been shutting down randomly and I have to switch it off at the power board to get it back on again. Also, its not cooling the room very well at all, though it seems to work a bit better at night.
Anyway, I found the error code on my remote. It was F3 - Outdoor abnormal discharge temperature. Can anyone tell me what's involved with this and how to fix it?
-
16-11-2008, 08:50 AM #2
Re: Daikin Inverter error code F3
F3 usually means loss of refrigerant-this also ties in with the lack of cooling.
get an engineer out to fix and recharge
Multisync
london
-
16-11-2008, 11:35 AM #3
Re: Daikin Inverter error code F3
Thanks for the advice.
-
16-11-2008, 01:50 PM #4
Re: Daikin Inverter error code F3
I agree with multisync, normally means a refrigerant leak. Get the installers back to repair under warranty if it's under 5y/o, you knew who the installers were, and you have receipt.
-
17-11-2008, 02:49 PM #5
Re: Daikin Inverter error code F3
one other thing to check is see if a "KRP" relay has been fitted to any of the indoor units and if its connected to any remote start/stop, fire panel or status monitor. reason being that for some reason the unit can be remotely shutdown and the f3 code appears but this only effect the indoor unit that the krp is connected to. strange but seen it happen twice now.
best of luck.
-
17-11-2008, 08:14 PM #6
Re: Daikin Inverter error code F3
New one on me!
That's like saying - sometimes when I switch the unit off it faults to F3.
Remote stop/start does not, in my opinion, cause fault codes.
The KRP is not a 'Relay' by the way - it is an 'add on pcb adaptor' capable of various functions, remote stop/start being one.
-
23-11-2008, 08:24 PM #7
Re: Daikin Inverter error code F3
it will not be the krp board at all if one fitted, you are looking at short of gas or over charged or nitrogen or blocked condenser coil..
Similar Threads
-
daikin L0 inverter problem
By robin r33 gtr in forum Air ConditioningReplies: 17Last Post: 11-03-2010, 11:25 PM -
daikin vrv inverter compressor check
By sunilkumarhvac in forum New TechnologiesReplies: 11Last Post: 23-11-2008, 03:00 PM -
Daikin Comp and inverter
By WCC73 in forum Air ConditioningReplies: 5Last Post: 08-11-2008, 08:44 PM -
help with daikin inverter
By johnjs in forum Air ConditioningReplies: 2Last Post: 17-09-2008, 07:06 PM -
Problem with an inverter compressor in V.R.V system DAIKIN R 407
By Harris Greece in forum Air ConditioningReplies: 10Last Post: 24-11-2007, 12:53 AM