Results 1 to 12 of 12
Thread: 460 volt 1 phase motor?
-
12-11-2008, 04:47 AM #1
460 volt 1 phase motor?
Hi,
I have some motors that are rated 460 volt 1 phase 60 Hz. I understand the more common voltage source is 460 volt 3 phase. So how does one obtain 460 volt 1 phase?
Can anyone tell me more about this or direct me to some links with more information on this?
Thanks
-
12-11-2008, 05:03 AM #2
Re: 460 volt 1 phase motor?
does it say one phase? or just 460V
because if it's 460V then you're probably going to hook it up to 2 phases.
-
12-11-2008, 05:50 AM #3
Re: 460 volt 1 phase motor?
It did mentioned 1 phase.
Some of the motors are reversible.
Also menitoned are the capacitors required.
-
12-11-2008, 05:52 AM #4
Re: 460 volt 1 phase motor?
best idea would be to get info from the manufacturer. or to look up a wiring diagram for it from google.
what brand and model number is the fan?
-
12-11-2008, 06:04 AM #5
Re: 460 volt 1 phase motor?
One of the motors is GE 5KCP39SGL794S.
Others are Carrier models HC52VE463, FH1076 and HC45SL460.
I have tried searching the net for wiring diagrams for any motors that are rated 460 volt 1 phase but cannot find any.
-
12-11-2008, 07:03 AM #6
Re: 460 volt 1 phase motor?
-
12-11-2008, 08:02 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 460 volt 1 phase motor?
It is still one phase even you connect it between two phase of power supply.
Two phase would be if you connect it like this: phase1-0-phase2.
In three phase power supply you have line and phase voltage. Line voltage is between one phase and earthed 0 from transformer. Phase voltage is voltage obtained between any 2 phase of power supply. What you need is phase voltage of power supply and, by connecting it between any of 2 phases it doesn't mean that you have 2 phase motor.
Direction of rotation with Permanent Split Capacitor is determined by placing condenser at one or another winding of motor, but if motor have one winding of lower resistance, than other winding is "phase shifting" winding, and only he could get his supply thru condenser, and rotation direction could not be changed electrically.Last edited by nike123; 12-11-2008 at 08:17 AM.
-
12-11-2008, 11:33 AM #8
Re: 460 volt 1 phase motor?
Yes, but remember that you will have two lives, instead than one live and one neutral.
-
12-11-2008, 05:30 PM #9
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
12-11-2008, 05:44 PM #10
Re: 460 volt 1 phase motor?
do you mean monophasic (one phase )460vac????i did't hear about this...i work on 115 vac(monophasic),220-230 vac(monophasic and threephasic),380vac (threephasic),440vac (threephasic) and 6600vac (threephasic)...
Maybe you have 3 phase and one neutral+ ground(erth conection)...or who know maybe you're right!
Mihai
-
13-11-2008, 02:37 PM #11
Re: 460 volt 1 phase motor?
There's a big difference. In a single live wiring, one fuse or single pole protection switch is enough. In a two lives wiring, you have to use two fuses or two single pole protection switches.
If the wiring in the electric box doesn't have bipolar protection switches or fuses, it is UNLAWFUL to connect two live conductors.
-
13-11-2008, 03:37 PM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 460 volt 1 phase motor?
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
3 phase motor
By mostafa_bostan in forum ElectricalReplies: 7Last Post: 07-01-2008, 08:36 PM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
dual voltage fan motor
By bill1983 in forum ElectricalReplies: 16Last Post: 09-05-2007, 10:36 PM -
locked rotor amps (LRA)
By vinod in forum Technical DiscussionsReplies: 16Last Post: 09-09-2006, 12:50 AM