    Cool Walk-In HELP!!!



    I did a ****ty job explaining this the last time so here it is. I have a walk-in refrigerator that freezes intermittently. I've changed the t-stat and still does the same thing. I'm wondering if it the way the t-stat bulb is placed.
    PLEASE HELP!!



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-In HELP!!!

    Quote Originally Posted by platinumfreeze View Post
    I have a walk-in refrigerator that freezes intermittently.
    I'm visualizing a walk-in refrigerator that has transformed the entire box into a huge block of ice. Or perhaps you are saying that the coil is frozen. Or maybe the lines are frozen. Or maybe there is frost on the ceiling... or maybe on the floor... or maybe something I haven't thought of is frozen?
    Last edited by Gary; 16-10-2008 at 08:47 PM.

  3. #3
    Join Date
    Aug 2008
    Location
    USA
    Age
    44
    Posts
    34
    Rep Power
    0

    Re: Walk-In HELP!!!

    It freezes the food intermittently.

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-In HELP!!!

    Where is the thermostat bulb placed?

  5. #5
    Join Date
    Aug 2008
    Location
    USA
    Age
    44
    Posts
    34
    Rep Power
    0

    Re: Walk-In HELP!!!

    The original t-stat control was mounted inside the the walk-in and the bulb was not mounted, just hanging. When I replaced the t-stat I mounted the control on the outside about 10" right of the door and ran the cap tube through the walk-in wall and around the edge of the evap box. The bulb is mounted to the evap box but not touching the evaporator, its not in direct air flow from the 2 evaporator fans. I hope that describes it enough, I'll go to the restaurant and take a picture if you want. Thanx

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-In HELP!!!

    The bulb should be sensing the air flowing into the coil... but not too close to the coil... kinda hanging in the air.

    What are the settings on the thermostat... both setpoint and differential?
    Last edited by Gary; 17-10-2008 at 04:55 AM.

  7. #7
    Join Date
    Aug 2008
    Location
    USA
    Age
    44
    Posts
    34
    Rep Power
    0

    Re: Walk-In HELP!!!

    It's set at 52-44 F differential of 8 degrees. The owner says when he gets there in the morning all the vege's and meat are frozen and sometimes a few beers have busted.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-In HELP!!!

    Also, the cap tube must be above the sensing bulb. Mounting it upside down drives the liquid portion of the charge out of the bulb, into the cap tube, possibly even back into the control.
    Last edited by Gary; 17-10-2008 at 05:14 AM.

  9. #9
    Join Date
    Aug 2008
    Location
    USA
    Age
    44
    Posts
    34
    Rep Power
    0

    Re: Walk-In HELP!!!

    Is the control damaged permanently if that occurs? I'm going to relocate it tomorrow. Thanx

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-In HELP!!!

    No, there is no permanent damage. Once the bulb is right side up and in a cool area the liquid will migrate back to the bulb.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-In HELP!!!

    Hopefully this will solve the problem, but if not you may need to move the control inside the walk-in.

  12. #12
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Walk-In HELP!!!

    platinum freeze,
    is the walk in chiller space has a walk in freezer door or has a partition panel for freezer?

    regards,
    abet

  13. #13
    Join Date
    Aug 2008
    Location
    USA
    Age
    44
    Posts
    34
    Rep Power
    0

    Re: Walk-In HELP!!!

    No, just a 10'x10' walk-in refrigerator.

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Walk-In HELP!!!

    How are the goods arranged inside?

    Does the air from the evaporator blows directly in to the frozen goods?

    Does the goods who are not in direct path of the air also frozen?

    What is TD of evaporator? What is the temperature of the air in and out of the evaporator. In the same time, what is the temperature near the termostat bulb?

    Did you checked with thermometer correct function of the thermostat regardless of being new?
    Last edited by nike123; 18-10-2008 at 08:45 AM.

  15. #15
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Walk-In HELP!!!

    I have had a few sticking contactors over the years causing the unit to run continiously.

  16. #16
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: Walk-In HELP!!!

    Quote Originally Posted by Andy W View Post
    I have had a few sticking contactors over the years causing the unit to run continiously.
    Yes that is a good point Andy makes .

    Have you ever seen the unit cycle off via the Thermostat ?

    Get rid of the old mechanical stat and fit a Danfoss EKC , Carel IR33 or Dixell and make sure you run these through
    a mini contactor so the load doesnt go through control. They sya they can handle the amperage but they never do
    in the long run .
    Last edited by Toolman; 02-11-2008 at 01:31 AM.
    60% of the time it works everytime.

  17. #17
    Join Date
    Aug 2008
    Location
    USA
    Age
    44
    Posts
    34
    Rep Power
    0

    Re: Walk-In HELP!!!

    Thanx for all the input!!! I used a number of suggestions. I repositioned the T-stat bulb, redirected the air flow and also changed the wiring around so the load from the compressor was not gong Through the T-stat.

    I remember thinking about the contacts sticking in the T-stat, but I ruled it out because it was new and figured it was bulb placement. Anyway it's been working great and the temp is consistent all around the box. THANX AGAIN!!!!!
    Smart remarks come from smart people.

  18. #18
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Walk-In HELP!!!

    Thank YOU for giving us an update! So few give the apretiation to say how the advice turned out. We love to hear of success

Similar Threads

  1. walk in freezer
    By ail in forum Refrigerants
    Replies: 8
    Last Post: 29-11-2009, 11:44 PM
  2. walk in cooler EVAPORATOR coil icing up
    By kurt854 in forum Fundamentals
    Replies: 5
    Last Post: 14-06-2007, 07:28 PM
  3. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Replies: 10
    Last Post: 02-11-2006, 11:56 AM
  4. It's snowing in my walk in freezer!
    By Matt in forum Commercial
    Replies: 19
    Last Post: 14-10-2006, 07:07 AM
  5. walk in Chiller--website
    By nik in forum Fundamentals
    Replies: 9
    Last Post: 23-06-2006, 07:46 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •