    Question fujitsu auy25r



    hi guys,

    i have been asked to move a fujitsu unit ,but being more familiar with mitsi units ,i was wondering about pumping down the fuji unit. i front seated the the high pressure side and ran the unit until the compressor switched off,however when i back seated the valve to to check if it would restart,nothing happened. Does this mean that there is something that needs to be reset,because the wiring diagram doesnt show a low pressure cut out
    any ideas?



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: fujitsu auy25r

    No, they don't have pressure sensors, just pipe thermistors.
    Did you move the indoor or outdoor?
    Recheck your wiring I guess, or you've just been unfortunate enough to have a break down after you've touched it last
    Indoor work OK? Any fault lights?
    Was it a 3 wire system (L-N-signal) or 5 wire system (L-N-comp-fanH-fanL-r/v)?

    edit: wait, just realised you hadn't moved it yet, plus one glaring thing:
    You said you front seated the valve until the compressor turned itself off?
    They don't turn themselves off. If you didn't switch of the isolator yourself after the suction got to 0kPa, something else made it cut out. ie t/stat, discharge thermistor, overload etc.
    You are not supposed to run them until they turn themselves off. You're supposed to turn them off youself when the suction pressure gets to 0kPa as there is no pressure control.
    Last edited by paul_h; 02-11-2008 at 11:51 AM.

  3. #3
    viking632's Avatar
    viking632 Guest

    Re: fujitsu auy25r

    thanks paul ,,

  4. #4
    viking632's Avatar
    viking632 Guest

    Re: fujitsu auy25r

    thanks paul, the unit is is 3 wire system, but i think you have answered my question there. looks like i need to look at the thermistor then.no fault lights are showing,do you have any test voltages?

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: fujitsu auy25r

    Quote Originally Posted by viking632 View Post
    thanks paul, the unit is is 3 wire system, but i think you have answered my question there. looks like i need to look at the thermistor then.no fault lights are showing,do you have any test voltages?
    Check compressor windings with ohmmeter! Check that power is supplied to compressor!

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. Fujitsu Window unit Size 9 same size as 6 ?
    By S_Line in forum Air Conditioning
    Replies: 1
    Last Post: 19-09-2008, 01:05 PM
  3. Fujitsu PCB
    By gwilliamson in forum Air Conditioning
    Replies: 6
    Last Post: 10-09-2008, 10:27 PM
  4. Fujitsu or not?
    By LRAC in forum Air Conditioning
    Replies: 14
    Last Post: 29-08-2007, 09:45 AM
  5. R22 Fujitsu FCUs on new Inverter Multi-Condenser?
    By Makeit go Right in forum Air Conditioning
    Replies: 3
    Last Post: 09-01-2007, 11:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •