    sakchai21's Avatar
    sakchai21 Guest
    How to find NH3 hermetic pump
    Which parameter have been considered? or only I just focus to total plant capacity.
    How can we select the NH3 hermetic pump in the correct way. Or anyone has any link to explain for this?Thanks in advance.
    Aug 2005
    5,302
    Re: How to find NH3 hermetic pump
    Here is a link to some basic information...
    http://www.cornellpump.com/industrial/refliterature.htm
    sodielectric's Avatar
    sodielectric Guest
    A pump manufacturer will need the capacity (GPM), differential pressure (PSI), and temperature to make a pump selection for you.
    Make sure the pump has an NPSHr around 1.5 to 2 ft less than NPSHa.
    May 2008
    Singapore
    First to size a NH3 pump you need the flow speed (m/s), next you will need the meter head (m) this is how to calculate.
    eg. if I have got 20 m vertical pipe from the pump, 100m horizontal after that. You will have to do this. (100 X 0.15) + 20m = 35m(head). The reason for using 100 X 0.15 is considering the friction loss on the pipe when it is running horizontally. For vertical you will need to use the full quantity. For the above, please consider the last evaporator the pump has got to pump.
    Flow speed, normally from a pump vessel outlet we size the outlet to about (0.5m/s) on the outlet before the pump. But after that you will need to consider the flow neeeded to reach the last evaporator.
    Lastly, a NH3 pump system is when u size 4:! circulation. This is the best.
    May 2008
    Singapore
    Tell you what, PM me your e-mail I send you a sizing chart from Hermetic-pumpen to size your NH3 pump
    Jun 2006
    jiansu
    38
    hi,
    tell me some details,I can help to select the correct ammonia pump.
    http://www.worldbase.cn/introduce1.html
    Jul 2005
    SOMEWHERE IN THE PLANET
    67
    Flow rate adn the head,available power supply.That's all you need.
    Feb 2008
    Lima - Peru
    42
    49
    "First to size a NH3 pump you need the flow speed (m/s), next you will need the meter head (m) this is how to calculate.
    eg. if I have got 20 m vertical pipe from the pump, 100m horizontal after that. You will have to do this. (100 X 0.15) + 20m = 35m(head). The reason for using 100 X 0.15 is considering the friction loss on the pipe when it is running horizontally. For vertical you will need to use the full quantity. For the above, please consider the last evaporator the pump has got to pump."
    what about pressure drop for fittings and valves.
  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Last Post: 20-05-2011, 02:18 AM
  2. Help with condensor pump
    By Bakerbj in forum Air Conditioning
    Last Post: 14-06-2009, 12:39 AM
  3. frostles heat pump
    Last Post: 31-03-2008, 07:53 AM
  4. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Last Post: 29-01-2008, 09:27 PM
  5. do we need a hermetic or semi hermetic comp.?
    By duraid in forum Fundamentals
    Last Post: 17-04-2007, 05:52 PM