    hi i'm abit new to the trade,i've got a prestcold l300 with 50 ish psi suction,and the head is getting very hot and leaking head bolts.is it possible to referb the head or tell the owner he needs a new one.would listen any help.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: hot,prestcold ?

    Is the compressor pumping ok? If the system is short of refrigerant the compressor will run hot. If it is not pumping ok (leaking valves or blown head gasket) this will make it run hot also.

    If it is pumping ok, but is just leaking refrigerant from the head bolts then you can replace the head and valveplate gaskets.

    If the compressor is not pumping properly and has been running hot for a long time (i've seen compressor bodies warp due to overheating) or has a lot of hours on it, which is likely will an 'L' body prestcold i'd be fitting a new or rebuilt compressor.
    I would also have a look at the fins on the condenser as if these are in poor condition it may be a better option to replace the whole condensing unit.
    What refrigerant is it running on? Whats it cooling?

    Jon
    Last edited by monkey spanners; 07-09-2008 at 06:51 PM.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: hot,prestcold ?

    The best way to check the valves is to shot the suction, force the compressor to run to the deepest vacuum and stop it.
    If it holds vacuum, than its OK and just need to check the valve plate gaskets. If not, open the head and see if it is a broken valve or gasket.

    If it gets too hot, there must be a problem.....

  4. #4
    Join Date
    Sep 2008
    Location
    uk
    Age
    57
    Posts
    5
    Rep Power
    0

    Re: hot,prestcold ?

    hi,it is on 134a,and should be cooling fres herbs,thanks for the advise.

  5. #5
    Join Date
    Sep 2008
    Location
    uk
    Age
    57
    Posts
    5
    Rep Power
    0

    Re: hot,prestcold ?

    hi,i tried pumping it down and it realy struggled to drop into a vacuum.broken suction valves?thanks for the help.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: hot,prestcold ?

    Sounds like worn valves. Sometimes after the compressor has been off for a few minutes you can here the valves whistling if they are worn.
    Sounds like its time for a new/rebuilt compressor or new unit. If you go for this why not take the head off of the old one before it goes to the rebuilders and have a look at how they work just to see.

    Jon

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: hot,prestcold ?

    hi tell me what type of gas its on + whats the head pressure