    charging a cap tube no data



    whats the best way to charge a capilary system with no data?is it by subcooling?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: charging a cap tube no data

    Yep, sure is; at least then you know that you have liquid at the start of the cap tube.

    Providing there aren't any major pressure drops between the condenser and the cap tube.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: charging a cap tube no data

    Assuming there are no airflow problems:

    When the refrigerated space is down to design temperature, the subcooling should be no more than 15F and the compressor inlet superheat should be about 20-30F.
    Last edited by Gary; 15-10-2008 at 07:49 PM.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: charging a cap tube no data

    Quote Originally Posted by roadking View Post
    whats the best way to charge a capilary system with no data?is it by subcooling?
    Some sources said by superheat! I following this source.

  5. #5
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    18

    Re: charging a cap tube no data

    Quote Originally Posted by Gary View Post
    Assuming there are no airflow problems:

    When the refrigerated space is down to design temperature, the subcooling should be no more than 15F and the compressor inlet superheat should be about 20-30F.
    Two problems

    1 How do you know how much gas to put in to get to the design temperature (it's a bit chicken and egg, which comes first the charge or the design temperature??????????)

    2 Most cappillary systems don't have any means of accessing high side pressures, which makes subcooling readings difficult to get.

    CB

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: charging a cap tube no data

    Quote Originally Posted by chillyblue View Post
    Two problems

    1 How do you know how much gas to put in to get to the design temperature (it's a bit chicken and egg, which comes first the charge or the design temperature??????????)
    All you can do is get it in the ballpark and wait.

    Quote Originally Posted by chillyblue View Post
    2 Most cappillary systems don't have any means of accessing high side pressures, which makes subcooling readings difficult to get.

    CB
    Make a 3 inch cardboard disk. Poke a hole in the center. Hold the cardboard disk up against the center of the condenser fins (don't crush the fins) and insert your temp sensor through the hole. This will give you a pretty fair estimate of condensing temp.

    An alternative is to check the temp of the return bends on the end of the condenser (two or three bends from the top)
    Last edited by Gary; 16-10-2008 at 08:30 PM.

  7. #7
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    18

    Re: charging a cap tube no data

    Nice one, thanks Gary.

    CB

  8. #8
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: charging a cap tube no data

    Quote Originally Posted by chillyblue View Post
    Two problems



    2 Most cappillary systems don't have any means of accessing high side pressures, which makes subcooling readings difficult to get.

    CB
    Go to NRS/HRP as they have copper driers with 1/4 inlet / capillary outlet with a schraeder connection on it. I use these all the time as when you cut the old one out you can cut the cap tube end off and connect it and use the schraeder connection with youre lines to blow through the system with OFN so as to make sure there are no blockages. If OK the cat the 1/4 end off and fit it to the inlet pipe from the condenser. Not sure of the part numbers and its too cold to go out to the van and get them tonight but the suppliers keep 100's of them at each branch

  9. #9
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: charging a cap tube no data

    As others said, and worth repeating: Fire in gas till you hear the cap tube start spraying liquid, you'll notice a sharp drop in temp on the evap plate, at which point let the fridge cool to temp then adjust charge for 20k of super heat.

Similar Threads

  1. Cap Tube Design Program - Results
    By Chef in forum Fundamentals
    Replies: 3
    Last Post: 01-09-2008, 09:49 AM
  2. Homemade charging tube
    By Tocoldtohold in forum Tools and Calculators
    Replies: 12
    Last Post: 02-12-2007, 02:25 AM
  3. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Replies: 4
    Last Post: 15-11-2007, 06:03 AM
  4. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  5. Finned tube data
    By Steve Wright in forum Fundamentals
    Replies: 5
    Last Post: 12-09-2005, 03:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •