Results 1 to 10 of 10
    Feb 2008
    Lima - Peru
    42
    49
    vertical recirculator vessel
    hi Guys:
    I have a problem, i'm checking a installation of liquid overfeed system of ammonia, and I found that the vertical recirculator is more small of the symtem need. what is the better solution for this problem?
    I hope you may help me.
    Best regards.
    Aug 2005
    5,302
    Re: vertical recirculator vessel
    What do you mean the vessel is too small?
    What problems do you see?
    Feb 2008
    Lima - Peru
    42
    49
    US ICEMAN:
    I think the vessel is too small because when the sytem is in defrost ( hot gas defrosting ) the system stop for high level of liquid and the pump begin and cavitate, i attach the sketch of vessel, the operating contions are:
    LOAD: 73 700 Kcal/h
    Circulate rate: 4
    Refrigerant: R 717
    there are 4 evaporators ( the hot gas defrosting consider 2 evaporator at the same time)
    Evaporating temperature: -25ºC
    Pump: Q = 1.37^3/h
    rP = 38.5m
    what do you suggest me?
    Feb 2008
    Lima - Peru
    42
    49
    Sorry¡¡¡¡
    I forget attach drawing of vessel.
    Attached Files Attached Files
    Aug 2005
    5,302
    Quote Originally Posted by luissandoval
    ...the system stop for high level of liquid and the pump begin and cavitate.
    If the liquid level is high, then what causes the pumps to cavitate? Normally, the higher the liquid level is above the pump suction the less problems you have with cavitation.
    Are the compressors shutting off when high level is reached?
    Feb 2008
    Lima - Peru
    42
    49
    For this system we used a compressor frick (screw compressor) because the compresor exists in the plant this compressor have a capacity of 145 000 Kcal/h and the compressor shutting off when high level is reached. the suction pump is of 1 1/2" of diameter.
    Aug 2005
    5,302
    When does the pump cavitate?
    India
    688
    What is the defrosting circuit? Since there is enough liquid in the vessel, it should not give any problems for the pumps.
    Valrico, Florida
    509
    How many evaps are you defrosting at once? How long has this been going on? What has changed in the system to start this problem? So many questions, not enough information.
    3,365
    Maybe to much load is taken off compressor to quickly at time of defrost and compressor cannot unload quick enough ?
    Could try a long pump down on evaporator eg 15-20 mins.
    Also check compressor can unload fast enough so as pressure does not
    drop to fast causing possible cavitation.
    Evaporators not on defrost have to be running and LLSV must be energized to circulate liquid all the time .
    It looks like compressor is a bit bigger than required so it may need to be loaded up pretty slow so as not to over shoot .
  1. oil return in a dunham bush vertical skrew
    By pauly-wog in forum Trouble Shooting
    Last Post: 15-10-2008, 07:47 AM
  2. Vertical Insulation freezer panels
    By samiam in forum Industrial
    Last Post: 07-05-2008, 05:03 PM
  3. Vertical header/collector
    By herdian in forum Technical Discussions
    Last Post: 14-08-2007, 08:25 AM
  4. accumulator (vertical gas/liquid separator)
    By omer26 in forum Domestic
    Last Post: 17-07-2007, 12:10 PM