    what can cause a system which has suction 26PSI discharge 195 psi and 28F at the end of tvx to go to > 60 F when you add refrigerant to it that give suction 44 psi and discharge 225 psi
    Apr 2001
    79
    5,071
    35
    Re: temp out of control
    Your question doesn't make any sense. Try again.
    Split Croatia
    6,151
    Who gives you this "academic" questions.
    Maybe, if you present them in original form, you end up with right answers much faster.
    haiti
    I restart the system but it stay at 52F
    i try to be short but it's the original form
    May 2008
    66
    802
    where you have 52F??? evap?? condensor outside ?? before TEV or after ??? more info please
    Ice
    haiti
    after TEV. Condenser outside . subcooling 3.33F. superheat -5F
    haiti
    after TEV. Condenser outside . subcooling 3.33F. superheat 45F
    Split Croatia
    6,151
    Quote Originally Posted by Gary
    For a proper evaluation, we need the following information:
    Low side:
    Evap air in temp
    Evap air out temp
    Saturated suction temp (SST) converted from pressure
    Suction line temp at evap outlet
    High side:
    Cond air in temp
    Cond air out temp
    Saturated condensing temp (SCT) converted from pressure
    Liquid line temp at receiver outlet
    __________________
    Or, if you prefer graphical representation of system something like this:
    http://www.refrigeration-engineer.co...ad.php?t=15303
    haiti
    This is a kind of chiller (pool) but water is not flow out.
    Without load on it we find
    Liquid line 96 F
    Suction line 65 F
    Condenser 89.6 F
    Climate 93.2 F
    Saturated Suction 5.2 F
    Saturated condensing 101 F
    Sep 2008
    kent
    52
    8
    what is the application?
    whats the gas?
    Split Croatia
    6,151
    Cond air in temp?
    Cond air out temp?
    What is "condenser" and "climate"?
    What you mean by "but water is not flow out"?
    If "climate" is ambient air temperature and "condenser" is condenser air out temperature, than that numbers doesn't make sense!
    What you mean "without load"?
    haiti
    gas r22
    water chiler
    climate temp is the temp arount the system
    condenser temp is the temp i found on the oposite face of the conderser blower
    Split Croatia
    6,151
    Quote Originally Posted by payoute View Post
    What you mean by "without load"?
    Describe evaporator!
    Why I have feeling like I am pulling informations you hesitate to give?
    Or it is language barrier?
    haiti
    the blower of the condenser is an aspiration one
    normaly the load is the water i want to cool . when it's empty i said it is without load
    Apr 2001
    79
    5,071
    35
    Liquid line 96 F
    Suction line 65 F
    Condenser 89.6 F
    Climate 93.2 F
    101F minus 96F = 5F subcooling.
    Add refrigerant until the subcooling is 15F.
    Then take all of these measurements again... with load.
    Split Croatia
    6,151
    Sorry, aspiration condenser is something I never heard or saw.
    How you move water around evaporator, or it moves naturally?
    Sep 2008
    kent
    52
    8
    have you got load on the cooler?
    i assume that you have a good water flow.
  1. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Last Post: 10-05-2008, 04:22 PM
  2. Compressor loading, cooling, and range of operation.
  3. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Last Post: 14-09-2007, 11:25 AM
  4. New Capacity Control Solution
    By embrown in forum New Technologies
    Last Post: 30-12-2003, 01:33 PM