Results 1 to 8 of 8
  1. #1
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    carrier split indoor fan speed low



    this unit is a high wall split indoor model 1C-841591KG7A.
    fault:fan motor nt blowin enough smetimes just slows down on its own.

    remedy:
    changed capacitor ----- no change
    changed remote reciever pc board ------no change
    this attempts done by other techs so far

    my diagnosis
    checked resistance of the windings:
    r -b =5.6
    r-o=4.5
    o-b=1
    r-red
    b-black
    o-orange
    motor ok windings resistance balanced
    there is another set of wires fro the motor to the pc board(indoor) labelled hall rpm snsor .
    I suspect the pc board might be faulty nt takin rite signal
    Can I go ahead n change the pc board ??
    hw does this hall rpm sensor work .
    the motor is a psc i guess



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: carrier split indoor fan speed low

    Hall sensors detect a break in a magnetic field, ie if you have a plate with a slot cut out of the edge, a hall sensor mounted near the edge could detect the slot cut and know how many rpms the plate is spinning. So the hall sensor is inside the motor.
    Cars with a distributor but electronic ignition use a hall sensor to fire the ignition coil.

    I take it you are testing the fan speed in fan only or cool mode, so the evap temp isn't limiting the speed in heat or auto mode?
    Did you check how much voltage is at the fan plug?
    If there's 240v there I'd suspect the motor.
    If there's not full voltage there, I'd suspect the PCB.
    If not sure, I'd say 80% PCB, 20% motor.
    Motors aren't expensive, less than the cost of a callback and further stuffing about

  3. #3
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: carrier split indoor fan speed low

    thanxs paul,fan motor was replaced by another tech so pcb left.So wats the purpose of hall sensors in arconditioners

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: carrier split indoor fan speed low

    Quote Originally Posted by bangoman View Post
    thanxs paul,fan motor was replaced by another tech so pcb left.So wats the purpose of hall sensors in arconditioners
    They pulse the motor in some circumstances, ie before heat starts, or in auto mode etc, so they want to know the fan speed.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: carrier split indoor fan speed low

    Check that correct wiring has done when fan has previously changed. Trace from PCB.
    On orange you should have neutral (common).
    On black you should have phase from solid state relay.
    On red you should have phase from fan condenser.
    If hall is wrong then you will probably have error announcement on LED-s.
    These fan behavior i found when fan leads are interchanged between start and run windings. Also, fan is rotating backwards and overheating, if that is the case.
    By the way, that was cause of my troubles in this thread.
    Last edited by nike123; 03-10-2008 at 11:15 AM.

  6. #6
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: carrier split indoor fan speed low

    indoor unit is 42100g fixed speed splits . the wires bn traced .ol ok no risk of miswiring the fan checked volt to fan motor ol ok

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: carrier split indoor fan speed low

    Quote Originally Posted by bangoman View Post
    indoor unit is 42100g fixed speed splits . the wires bn traced .ol ok no risk of miswiring the fan checked volt to fan motor ol ok
    When fan slows down do you have also voltage drop from PCB?

  8. #8
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: carrier split indoor fan speed low

    Ddnt check wen it last dd. Thing its intermittently so nt ol the time does it slow dwn

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier split not heating
    By philjd26 in forum Air Conditioning
    Replies: 1
    Last Post: 01-10-2008, 10:45 PM
  3. carrier split unit R22
    By airconadam in forum Air Conditioning
    Replies: 24
    Last Post: 06-11-2007, 11:22 PM
  4. the carrier split draw amper more than notmal
    By karimihassan in forum Air Conditioning
    Replies: 5
    Last Post: 19-08-2007, 12:20 AM
  5. York / Carrier/ Whirlpool ..split A/c
    By fireblade in forum Air Conditioning
    Replies: 2
    Last Post: 24-07-2006, 12:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •