Thread: Problem with plugged condenser
-
19-09-2008, 02:05 AM #1
Problem with plugged condenser
Insalled new 3 phase scroll compressor, R22 system.
the old one was rattling and making noise and not pumping.
now the new one runs fine for a minute and starts pumping down and all the sudden the high pressure internal safety valve on the compessor pops. the high side guage is only reading 180 psi at the discharge of the condenser. so this tells me the condenser must be plugged.
i backflushed the condenser with nitrogen today and nothing came out and seemed free from any kind of plug or chunks of anything.
also installed a shrader valve near the discharge of the compressor to check psi there but it sure seems like the condenser is plugged up. i will try running it again later and check the PSI just after the compressor on the discharge side..
any ideas?? i have a bad feeling its going to do the same thing even after i flushed the lines with nitrogen because they sounded clean and nothing came out.????????????????
-
19-09-2008, 09:03 AM #2
-
19-09-2008, 12:24 PM #3
Re: Problem with plugged condenser
yes tried that wirring is ok, pumping well as stated but internal pressure safety still pops. i will find out more very soon.
thank you though
-
19-09-2008, 06:15 PM #4
Re: Problem with plugged condenser
I've had a vibration eliminator collapse internaly and do something similar.
-
23-09-2008, 08:40 PM #5
Re: Problem with plugged condenser
hi kurt s
is it split a/c unit? u didnt mention brand of the unit. some unit has filters in indoor distibuter.if its 180 psig condersor outlet pressure then u r outdoor units is ok.plz check u r indoor unit
regards
dinesh shetty
-
24-09-2008, 05:17 PM #6
Re: Problem with plugged condenser
is this the comp you had problems with running the wrong way ?
-
02-10-2008, 06:01 PM #7
Re: Problem with plugged condenser
Have u compair old and new compressor's specification?
-
02-10-2008, 06:46 PM #8
Re: Problem with plugged condenser
if the outdoor unit comes whit a capillary,there must be a small filter and valve build to it. try to change the complete capillary set whit filter and reverse valve. it might work.
the filter and valve is a thicker tube at the end or beginning of the capillary and functions like a injector.
hope you now what i mean,pitty i don't have pictures at hand.
Ice
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
A strange problem
By MuhengineeR in forum Air ConditioningReplies: 14Last Post: 27-10-2010, 05:21 PM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM -
Condenser Length Problem
By tanveerkuet in forum Technical SpeculationsReplies: 5Last Post: 01-02-2008, 12:05 PM