    toshiba unit



    commissioning a new toshiba install with two indoor units rav -sm562krt-e and outdoor rav -sm1102at-e.Bth units nt cooling bt compressor running .back pressure is standing pressure like compressor nt running at all.Checked pumping efficiency ok. units running on R410A



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: toshiba unit

    Quote Originally Posted by bangoman View Post
    commissioning a new toshiba install with two indoor units rav -sm562krt-e and outdoor rav -sm1102at-e.Bth units nt cooling bt compressor running .back pressure is standing pressure like compressor nt running at all.Checked pumping efficiency ok. units running on R410A
    Check 4 way valve!

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: toshiba unit

    Quote Originally Posted by bangoman View Post
    commissioning a new toshiba install with two indoor units rav -sm562krt-e and outdoor rav -sm1102at-e.Bth units nt cooling bt compressor running .back pressure is standing pressure like compressor nt running at all.Checked pumping efficiency ok. units running on R410A
    What happened when you tested pumping efficiency, ie what did you do, what were the readings?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: toshiba unit

    Check valves are open.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: toshiba unit

    ??????? check valves or check the valves .No check valves on the unit just the 4 way reverse cycle valve

  6. #6
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    22

    Re: toshiba unit

    Hi Bangoman,

    I think Brian is saying check that the service valves are open.

    What compressor pumping test did you do? A pump down test? Or what?

    There are a couple of other things to check;

    1. Gas charge. Note these outdoor units are pre-charged for 30m as a single split but 20m if a twin split (18m main pipe and 2m branch) - so check your additional gas charge calculation.

    2. Wiring; this is frequently wrong. Outdoor to master indoor connections 12&3. Master indoor to slave indoor connections 1&2 only AND connections A&B. Optional connection A&B from Master indoor to wired controller. (You can use the supplied infrared controler but only communicates with master indoor).

    The common error is the '3' wire between master and slave - do not connect. If it has been you'll need to correct the connection and then re-configure the address set up (wired controller for this).

    I'd also suggest checking your pipe work isn't blocked - liquid line filled with brazed for example or a kinked pipe.

    Cheers

    Loops

  7. #7
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    22

    Re: toshiba unit

    Sorry should have asked what happens if you try heating mode?

    The reversing valve is energised for heating. If the valve hasn't settled fully one way or the other then energising to give heat may help.

    Cheers

    Loops

  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: toshiba unit

    Quote Originally Posted by bangoman View Post
    ??????? check valves or check the valves .No check valves on the unit just the 4 way reverse cycle valve
    If it's capillary or mech TX valve system, there will be check valves so the refrigerant goes "the right way". From the infomation you've given, check valves seem the most likely cause.
    Electronic TX valve systems often don't have check valves though.
    There's no way to test compressor pumping unless you can isolate the reversing valve anyway, as a faulty/stuck reversing valve will stop a compressor pumping down, hence my previous question, how did you verify the compressor pumping efficiency is good?
    Last edited by paul_h; 26-09-2008 at 11:15 AM.

  9. #9
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: toshiba unit

    thanks mates isolated the 4 way reverse cycle valve to find that its the culprit.stuck on heating mode .

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. New Toshiba unit won't start..?
    By expat in forum Air Conditioning
    Replies: 14
    Last Post: 07-04-2008, 09:11 PM
  3. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  4. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  5. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •