    Question No expansion valve???



    Hi guys

    This is my first post here and I gotta tell you that I don't know much about refrigeration.

    I have a doubt about a recent walk-in cooler that I got installed just today (finally).

    The walk-in cooler is aproximately 6 ft x 20 ft, 8 doors.

    Just one thing about it: When the tecnician was installing it, he said the expansion valve wasn't working right, so he took it away, I mean he conected it directly without the valve, and he says he's gonna use a timer.

    I don't know much, but that sounds fishy to me, like he's trying to save some money.

    I have strong reasons to doubt of the ethic of this guys, we gave 'em the 80% of the money for the walk-in cooler and they installed it in 5 months, only after we arrived at their local with 2 trucks full of cops (haha, courtesy of a cop friend).

    Anyway, that's life in Mexico but I'd like to know if that no-valve-only-timer things is just a cheap fix and I would end up paying later for that.

    Thank you.

    I hope I'm right posting this kind of question here.



  2. #2
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    71
    Rep Power
    17

    Re: No expansion valve???

    Never heard of that before??

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: No expansion valve???

    Anyway, that's life in Mexico


    Thats explains something but go know, you might be on the threshold of a new invention.

    Keep us posted how does it cool.

  4. #4
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: No expansion valve???

    Are you sure it was the expansion valve he removed? Its pretty darn crucial to the operation of the room. Does it get cold at all?
    ...and she said "give it to me you big fridgie"

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: No expansion valve???

    I believe that if the liquid line is 1\4, there will be some kind of pressure drop in the evaporator and therefore some cooling,

    The compressor will defiantly will be cold and the head pressure will be low.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: No expansion valve???

    If it was the exp. valve, then it will never work like it should Like 750Valve, one of the most crucial parts ion a refrigeration system.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    17

    Re: No expansion valve???

    This system cannot work as without the drop in pressure after the expantion valve(this is its function)there will be no evaporation hence no heat absorbed,the compresor just pumping refrigerant with no cooling effect.That is unless he replaced it with cappillary tube which I dout his being cappable to calculate its length and bore size.

  8. #8
    Join Date
    Aug 2008
    Location
    mexico
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: No expansion valve???

    Hi

    Thank you guys for all your responses.

    Following your comments on how it was not possible the cooling without the valve, I went to see what he did and aparentely he left the valve there, but added a few rings of cappillary tube as casstrig comented.

    All that is what I can see without openind the fan, I dont feel confortable opening it since he made some changes (the cappillary tube connected with some other hardware) and those changes look like they're gonna break if I force the lid of the fan open.

    The original valve was Danfoss, blue. I don't know if this would work, or if its recomendable the let it like that. It's is cooling, last night went all the way down to 30F and today its about 37F.

    The doors are all wet, from the condensation and thats because it's pretty hot down here, but we specifically told them we wanted heated doors but i just did some research on the trash where they put the wooden boxes and it says NHG: Non-heated-glass.

    Apparently I'm gonna have nightmares for a long time.

    Thank you all for your responses and please feel free to laugh at me

  9. #9
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: No expansion valve???

    I think buelldart is referring to a temperature control. It makes more sense on why the tech would state that a timer would work (which is not the case).

    The Danfoss TEV's we sell here the USA are not blue. The temperature controls are dark blushish/black.

  10. #10
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: No expansion valve???

    The Blue Danfoss component sounds like a solenoid coil to me.

  11. #11
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: No expansion valve???

    sounds weird and without an expansion valve it won't cool as you will get no pressure drop.....
    i think he is having you on...this will also cause your compressor to pump liquid.......ummm don't think it is the EXV..

  12. #12
    Join Date
    Jul 2008
    Location
    Southeastern US
    Posts
    11
    Rep Power
    0

    Re: No expansion valve???

    Stories like this make me cringe. Was this a Mexican refrigeration local? I wasn't even aware that fridgies were organized down there.
    As for the mechanic's actions; I can see replacing an expansion valve with cap tube, but as a temporary measure only. By your description, that doesn't sound like the case.

  13. #13
    Join Date
    Aug 2008
    Location
    mexico
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: No expansion valve???

    Hi guys, thanks for all your responses.

    I really don't know if it was only for temperature regulation or it was a replace for the valve that he added the rings.

    And yes it was a Mexican refrigeration local, since I'm in Mexico. I'm regreting it a lot, I can't trust anything of the work now. In a point we made them sign a 2-year warranty but from these guys, a 10-year warranty is worth 5 cents.

    One thing that's driving me crazy is the Non Heated Glass Doors. The condensation it's a lot.

    We're 90F with 50% humidity but still, i've had lots of fridges with glass doors and never seen anything like that.

    I took some pictures so you can see what I'm talking about, I just took them 5 minutes ago so the condensing unit pics are blurry since it's night time.



    I'm thinking on paying another refrigeration business to come and fix everything.

    Thank you guys for all your comments.

  14. #14
    Join Date
    Aug 2008
    Location
    mexico
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: No expansion valve???

    I'm not allowed to post links here but I'm gonna take a shot I hope it doesn't get deleted
    Attached Images Attached Images

  15. #15
    Join Date
    Aug 2008
    Location
    australia
    Age
    51
    Posts
    46
    Rep Power
    0

    Re: No expansion valve???

    there is no such related issueu between tx valve and timer. its look like that the tichnicain playing games with u.but in refrigeration there is timer that is responsable to defrost the ice of evaporator.

  16. #16
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: No expansion valve???

    I'll post a link up for you mate so all can see without typing the address.

    Well thats some pretty shoddy work right there, everything from the room construction to the way the drain is (not) secured, I especially like the way he hung the evaporator...

    http://s37.photobucket.com/albums/e6...view=slideshow

    Incidentally that is a heated door insert you can see the wiring label in one of the pictures -
    red - door heat circuit
    white/red - door heat neutral
    black - frame heat circuit
    white/black - frame heat neutral
    It is likely not wired up correctly if at all.


    Now that last pic where you indicate what he added - that IS an expansion valve (TXV) the rings are a part of the expansion valve. With the right amount of careful bending of the copper tubes that cover will go back on.
    ...and she said "give it to me you big fridgie"

  17. #17
    Join Date
    Aug 2008
    Location
    mexico
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: No expansion valve???

    Thanks 750

    Then the guy is playing games with me, unless he added that valve himself.

    About the wires.. yes I thought that myself but doesn't the door need to be wired too? those wires go in the frame, so I would expect that the frame is wired somehow to the door. Anyhow it's not working, either the wired it all wrong or only the frames are heated -- incidentally the frames sweat too.

    I added a few more pictures of the condensator.

    I think I'll call someone else to come fix this thing. It's a headache.

    Thanks again.

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: No expansion valve???

    If you not already paid him, then I should send him a letter stating that his job isn't done the way it should be.

    Never saw such a sweating doors.

    I should contact in this case immediately a lawyer.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: No expansion valve???

    I already see fungus on the doors.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: No expansion valve???

    Open any door, about halfway down on the hinge side of the door you shoul see a cable come out from the frame and enter the door - this is where the doors plug into the frame to get power to run the heaters, some have their power cords routed to the top of the door but most are halfway down the door on the hinged side.

    With hold any money you owe him and pay someone else to fix it, it may cost a little more but it sounds like you are dealing with a really dodgey individual. You'll have piece of mind knowing the job is done correctly.
    ...and she said "give it to me you big fridgie"

  21. #21
    Join Date
    Sep 2005
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: No expansion valve???

    doors need anti-sweat heaters and the frame on seperate circuit- as for operation of chiller how did he calculate load, size is very important. looking at pics evap could be flooding

  22. #22
    Join Date
    Aug 2008
    Location
    mexico
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: No expansion valve???

    I still "owe him" 2000 dlls. Of course I'm not gonna pay him. It's an absolut mess. Everything is wet, costumers can't see a thing.

    I sent an email to a sales rep of Anthony Doors to see if we can upgrade to heated glass doors. Of course, I would be dealing directly with AI.

    It's very frustrating...

  23. #23
    Join Date
    Dec 2007
    Location
    US ALASKA
    Age
    62
    Posts
    16
    Rep Power
    0

    Re: No expansion valve???

    Well gents I've seen a simple ball valve act as a TEMPORARY metering device in a reefer system.. It's crude indeed but will work in an emergency, you just crack it open a little to create that pressure drop... cheers, kooler

  24. #24
    Join Date
    Aug 2008
    Location
    stockport
    Age
    37
    Posts
    7
    Rep Power
    0

    Re: No expansion valve???

    without an expansion valve, you aint got a chiller. good luck

  25. #25
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    17

    Re: No expansion valve???

    wonder whats happened whit the LP/HP box ??
    insulation on the tubes s***s to.seeing stuff i would rather not be seeing. pallet for engine hosting looks nice, for now.wonder wat happens to the unit wen it becomes rotten.
    hope not all Mex techs are like that,ore the nightmare will only just begone.

    sorry for you M8,keep on fighting

    Ice

  26. #26
    Join Date
    Aug 2007
    Location
    UK
    Posts
    26
    Rep Power
    0

    Re: No expansion valve???

    I'd be contacting my solicitor.... the equiv . of HSE in Mexico and several of my largest friends to go and "see" him. For gods sake don't pay him anything else.

    I'd be ashamed to put my name to that install.

    And yeah 750.... the Evap hanging is the new Anti Vibration method!!!

  27. #27
    MOHAMMED ASHRAF's Avatar
    MOHAMMED ASHRAF Guest

    Re: No expansion valve???

    It is very surprise news from Mexico.any way pls wait and see final result.who is don't know about working of exp valve.

  28. #28
    tomfagan29's Avatar
    tomfagan29 Guest

    Re: No expansion valve???

    he's pulling your leg, thats for sure

Similar Threads

  1. Expansion Valve Selection
    By raviperumal in forum Technical Speculations
    Replies: 12
    Last Post: 17-02-2010, 09:58 AM
  2. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Replies: 10
    Last Post: 22-06-2008, 12:29 PM
  3. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Replies: 4
    Last Post: 08-06-2008, 06:52 PM
  4. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  5. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •