    Burst Pipe caused by Abrasion. (aka Only on a Friday)
    Another Story from the Grizzly Archives.
    The attached photo's are of a Copper pipe.
    That has had a hole worn through it whilst rubbing against a Steel Pipe. (also pictured)
    Nothing new in that I hear you say!
    True but this pipe was a 2 1/8" Discharge line feeding a remote Condenser approx 50mtrs away.
    The system charge was 80KG of R22.
    Also the Steel pipe which it was running across happened to be the 6" Gas main supplying the building boilers ECT.
    So it's Midday Friday last and I am in the basement of a large 4 storey Office Block. With the Site Engineer (Carrilion..they are everywhere nowadays!!)
    Looking at the Condensers and how many fans were running ECT.
    With the option in mind of maybe raising the system discharge pressure, to offset the fact that it was operating very close to it's LP Cut-out settings.
    Thereby buying some time whilst the system was leak checked and investigated to identify the cause!
    Anyway next thing we knew was that the building Fire Alarm was sounding and as we made our way back up through the Building.
    The cause became apparent.
    The system Discharge Pipe had finally let go filling the
    Plant Room on the level above us, together with it's Stairwell and several floors above that.
    With probably 70kg's worth of R22.... Ouch....
    It's Friday Dinnertime mind!
    Fortunately we were able to quickly gain access to the plant room and I was able to isolate the Discharge Line.
    But if you saw the size of the Condensers and the pipe runs you would understand why the System Dumped nearly all it's gas.
    The Building Ventilation soon took over and occupation was restored.
    So it's Friday,
    70 to 80 KGS of R22 has permeated around the whole building evacuating albeit temporarily the offices.
    (HM. Inland Revenue)
    Oh and I forgot the Carrilion H&S Rep was on-site.( He turned out to be a brilliant help!)
    All a recipe for disaster really!
    But I have to say Everyone was fantastic about it!
    As this system was at least 15 yrs old and everyone accepted that as they say "These things Happen!!"
    Grizzly
    Sorry Guys I forgot to upload the piccies.
    Had one of those days today. Sometime I will regale the story of the "CARTWHEELING TRANSIT DOOR"!
  2. #2
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19
    Re: Burst Pipe caused by Abrasion. (aka Only on a Friday)
    Grizzly, am I missing something? I dont see any pictires attached.
  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45
    (He must have had one of those senior moments...)
  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47
    Sorry Guys!
    Hopefully it's ok now?
    Grizzly
  5. #5
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16
    loving the unistrut bracket!
  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Don't you start knocking Carillion Grizzly, I'll have to set the lads on you
    Glad that you got on OK with our H&S chappie, they pretty 'on-the-ball'.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  7. #7
    Join Date
    Aug 2008
    Location
    Auckland
    Age
    55
    Posts
    259
    Rep Power
    21
    Surely not! Tell me its not true! It couldn't be! Has that refrig copper pipe been cut with a HACKSAW and is that swarf etc I see in the pipe........NEVER! Not by a subscriber to RE, Tell me ain't true........please please......
  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,703
    Rep Power
    47
    Quote Originally Posted by Brian_UK View Post
    Fair enough Brian,
    But just how many maintenance Companies have they "Acquired" in the last couple of years?
    OK Goober
    I Wondered how long it would be before someone picked up the Hacsawn pipework.
    1) I had forgotten my large pipe cutters.
    2) We needed to access the worn area to ascertain the "Damage". As it turns out the indent in the gas pipe is large enough. (sadly the pics doesn't show up how deep it is)
    To warrant further Investigation prior to the pipework being replaced.
    3) I have no intention of leaving that pipework in place. Even if I wished to I don't think the old Elf |& Safety, would allow me to braze in new joints near the Gas Pipe.
    So using a 3mtr length the joints will be well away.
    Looking at the piccies I am surprised there have not been other questions.
    I know I had plenty!
    Grizzly
  9. #9
    Brian_UK's Avatar
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Carillion have already eaten Planned Maintenance as well as Mowlem and earlier this year swallowed up McAlpine.
    Retired March 2015
  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46
    Nice one Grizzly
    I've had to resort to the faithful old hacksaw on a few occasions, i found that if you apply a little oil to the area as you cut the chips don't travel too far down the pipe.
    I did once use a holesaw to make a tee when i had gone into 'customer getting exactly what they asked for mode' but thats another story
    Jon
  11. #11
    Join Date
    Aug 2008
    Location
    Auckland
    Age
    55
    Posts
    259
    Rep Power
    21
    Heh Grizzly, I'd be lying if I said I'd never used a Hacksaw on fridge pipe!
  12. #12
    Join Date
    Jul 2008
    Location
    uk
    Posts
    150
    Rep Power
    16
    Quote Originally Posted by Goober View Post
    especially when its time to rip out the scrap
Similar Threads
  1. Mitsubishi PUHZ-RP200YHA Pipe Sizes
    By gwilliamson in forum Air Conditioning
    Last Post: 14-05-2008, 09:43 PM
  2. burst pressure standart for 410A
    By cakabo28 in forum Refrigerants
    Last Post: 14-02-2008, 06:21 PM
  3. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Last Post: 08-07-2003, 10:58 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts