Thread: thanks
    Mar 2003
    Tanzania(East Africa)
    59
    27
    thanks
    I am extremely happy to be one of the member of this group and I thank personally to MarkFiddy and chemicool for helping me out so fast. It was so nice of them and I think For tech like us in third world with little knowledge help is real something beyond words
    as my original question was like this
    I have problem with Carrier cassatte unit
    it blew compressor scroll type
    air con details are as follows
    model 40GKX 060 703 40
    CODE ZOO7655G04
    SERIAL 04AMI32309
    13.20 KW COOLING
    NOW I RECEIVED NEW COMPRESSOR SAME DETAILS BUT WITH DIFFERNT OIL (POE) NOW TROUBLE STATRS AS SOON AS I FILL UP ***** AND AFTER 3HRS i loose cooling and if i see my gauges low side it shows from 60 psi to 20 and high remains same 250 psi now i checked all details where could i go wrong i am using R 22 lubricant is RL 32h please help me
    thank you all
    can you believe me i found capillary blocked with oil an i heated up as said and changed oil after consulting South Africa supplier
    its just 100%.
    jay
    shogun7's Avatar
    shogun7 Guest
    POE oil is normally used with the newer HFC refrigerents like 410a so if you had mineral oil in the old compressor you could be having a situation where the 2 oils are mixing a causing the cap tube to plug up. Now you can use mineral oil, OR poe oil, OR alkylbenzene oil in an R-22 system BUT not to mix them.
    Jun 2002
    628
    Post thanks
    yes i did question jay regarding the oil issues
    Sep 2003
    ISRAEL
    72
    4,248
    hello jay,
    I'm glad all is well now.
    chemi
    Sep 2003
    ISRAEL
    72
    4,248
    jay,
    refrigeration oil is like an alcohol drink, when you mix them you get truble!
    chemi