Results 1 to 13 of 13
    Feb 2008
    Lima - Peru
    42
    49
    refrigerated load
    hi guys:
    I dont know how can i calcute the refrigerated load for a room is not rectangle, i attach the room's drawing. i have i program for selection but my program only calculates rectangle room. please help me.
    Attached Files Attached Files
    Nov 2005
    New Zealand
    550
    Re: refrigerated load
    Hi, you can calculate it by making numerous rectangles then add them up
    regards Norm
    Apr 2008
    Kent
    68
    surely that drawings not for one of your own jobs?
    Aug 2005
    5,302
    This is a good example of why it is important to understand how the calculations work. This example does not fit the parameters of the software, so the software is not entirely useful.
    The simplest way to solve this is to break up the areas into individual spaces/areas. Then sum the sub-totals of the individual spaces/areas.
    Feb 2008
    Lima - Peru
    42
    49
    US ICEMAN
    thanks a lot, but i have a question for calculate the refrigerated load i need to know the temperature outside the room.
    if i broke the area in several rectangles and i'm going to solve one. what temperature should i consider on the side that is inside the room? i think the temperature of the room. is that correct?.....
    Aug 2005
    5,302
    If one of the walls of the imaginary rectangle is exposed to the inside temperature of the space, the heat load for that wall is zero. The temperature is the same on both sides of the wall.
    Aug 2008
    Englewood, CO
    With a little trial and error you could make an equivalent rectangle with the same total area and the same perimeter. Then, feed these dimensions into the formula.
    Feb 2008
    Las Vegas, NV
    67
    330
    luissan,
    I agree with the others with one exception.
    This looks like a large warehouse storage facility. If my conversions are correct, the bottom vertical rectangle is approximately 27ft x 118ft x 29ft with dock doors.
    I would run at least two, if not three separate loads: bottom section, top right section and top left section.
    If that is dock doors on the bottom section, the air infiltration load will be high compared to the other sections.
    If your not comfortable running a load on this box, get some more experienced help. There will be extra load factors to consider ie: fork lifts, people (100), heat producing equipment if applicable, humidity conditions for a working enviroment, dock door factors (air curtains and usage time) etc.
    Aug 2005
    5,302
    Another point to be aware of is; the cooling capacity will have to be installed in the space to meet the requirements of the separate areas. The areas where the dock doors are located will have a significantly higher load than other areas. Therefore you will find these areas have the greatest concentration of cooling capacity that needs to be installed.
    If not, then some areas may be unable to maintain the desired temperatures.
    Oct 2005
    Romania
    44
    Hi , luissandoval
    You want to calculate the refrigeration load ( for coldroom ) or cooling load ( for conditioning area ) ? !4 C deg. means conditioning not refrigerations . Please , send us more informations .
    Gramcor
    Feb 2008
    Lima - Peru
    42
    49
    Gramcor:
    I want to calculate the refrigeration load for conditioning area.
    Oct 2005
    Romania
    44
    Hi , luissandoval
    If you have coldroom , you must calculate only refrigerations load. If you have conditionning , you must calculate cooling load and fresh air change for 100 persons ( about 20 - 40 mc / h per each person.
    gramcor
    Oct 2003
    5,630
    Multiply the U factor of walls and ceiling with the total surface and multiply it with the temperature difference and add the heat load of the products.
    That's it. Simply, isn't it.
  1. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Last Post: 28-05-2008, 01:08 AM
  2. Compressor loading, cooling, and range of operation.
  3. How is load divided between indoor units
    By mchild in forum Air Conditioning
    Last Post: 17-01-2008, 10:30 PM
  4. How to Design Refrigerated Cabinets
    By Rayin in forum Fundamentals
    Last Post: 26-11-2006, 08:27 AM
  5. AKV versus higher load
    By Peter_1 in forum Industrial
    Last Post: 18-04-2004, 11:05 AM