Working on a a/c unit(220volt).found a bad run capacitor.The original capacitor is a 35uf-440vac.replaced it with a 35uf-370vac(thats all I could find in-town).will going from a 440 to a 370 vac rating cause any problems?
Last edited by cretan; 15-08-2008 at 07:49 AM.
-
15-08-2008, 08:29 AM #2
Re: capacitor voltage?
When replacing failed capacitors, it is important to use capacitors having voltage ratings equal to or higher than those recommended by the motor manufacturer so if it's an OEM cap of 440 V then replace it with same
-
15-08-2008, 08:36 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: capacitor voltage?
Yes it could cause problems but that depend about operating conditions. Voltage of motor capacitor should be at least 130% of operating voltage and up. That value depends on many conditions but safety margin of double operating voltage is most often.
In your case, it could be OK. but that mean that you added one weaker point then it was before.
Check this!
-
15-08-2008, 08:56 AM #4
Re: capacitor voltage?
Thanks guys.I will replace it with the correct one.
-
17-08-2008, 03:09 AM #5
Re: capacitor voltage?
A Capacitor with a lower capacitance will increase the current on the running windings..Something to watch..