    What would you guys do?
    Hello guys, I've got a customer that has an old staycold upright double door display chiller. Compressor has gone-not pumping. Had a look round the system, the comp is a danfoss fr11 r134a, not original. I looked at the data plate and the charge weight was for R12, so its very old. I do not have a clue as to which gas it has in it at the moment, nobody has written the gas type on it anywhere.
    I have nearly talked him into spending on a new cabinet but when he found out the modern day equivalent was £1100+ he was less than impressed.
    What I need to decide, if he wants to go ahead with the repair, is whether to get the R12 version of the comp and fill it with fx56 or get the r134a version and sick with r134a.
    Andy
  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Re: What would you guys do?
    capillary or TEV?
    Anyhow, if you tell your customer that within 1.5 year you no longer will find FX56, then that's his decission to let it repair
    If it's capillary and you want to convert it to R134a, the ther must be cut of a piec eof the capillary.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46
    R134a compressor and R413A (R49) would be my choice if he wouldn't go for a new chiller.
Similar Threads
  1. hey guys
    By ScottG in forum New to RE
    Last Post: 11-06-2008, 07:58 PM
  2. Are we all fridge guys?
    By LRAC in forum Chit Chat & Service Stories
    Last Post: 20-05-2007, 10:39 PM
  3. Hi Euros, I found you guys on HvacCommunityNetwork.com
    By isitfixedyet in forum New to RE
    Last Post: 24-04-2007, 10:46 PM
  4. hi guys
    By milton in forum Industrial
    Last Post: 30-03-2004, 07:41 AM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts