    cellar cooler not cooling



    Hi have been working on a IMI celler cooler today customer had said it was not cooling. On arrival found room temp. to be 10-12c think this is about right but found coil tempture on evaporator at bottom to be 0c and the top at 12c ??? System is a 407c and took suction pressures at 55psig. Condensor fan seems to be running at full speed todays outdoor temp 20c. Is the system short of gas or is there a problem with the expansion device may be partial blockgage any ideas? thanx



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: cellar cooler not cooling

    Quote Originally Posted by mknight View Post
    Hi have been working on a IMI celler cooler today customer had said it was not cooling. On arrival found room temp. to be 10-12c think this is about right but found coil tempture on evaporator at bottom to be 0c and the top at 12c ??? System is a 407c and took suction pressures at 55psig. Condensor fan seems to be running at full speed todays outdoor temp 20c. Is the system short of gas or is there a problem with the expansion device may be partial blockgage any ideas? thanx
    Dear mknight

    No offence, but what are you doing working on a cellar cooler if you don't know the basics??

    Taking superheat readings,among other things, will tell you if it's short of gas.

    Are you a trainee just out on your own?

  3. #3
    Join Date
    Jul 2008
    Location
    southampton
    Age
    52
    Posts
    5
    Rep Power
    0

    Re: cellar cooler not cooling

    sorry Frank not been to school for 10 years+ been split bashing ever since forgoten more then i can remeber!

  4. #4
    Join Date
    Oct 2005
    Location
    england
    Age
    43
    Posts
    5
    Rep Power
    0

    Re: cellar cooler not cooling

    alot of the IMI units have the exp device just after the liquid service valve at the outdoor unit they have a little orifice inside. Pump the unit down and take it apart, its on flare nuts sometimes they get crap inside them.

  5. #5
    Join Date
    Oct 2007
    Location
    leeds
    Posts
    76
    Rep Power
    17

    Re: cellar cooler not cooling

    You say the temp in the cellar is 10-12c?That the perfect tempreture.
    What makes you think its short of gas?have you checked the sightglass,is the evap icing up?

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: cellar cooler not cooling

    As Frank says, you need to take the temperature of the suction line and work out the superheat. This will tell you if the unit is short of refrigerant or if there is a blockage.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: cellar cooler not cooling

    Quote Originally Posted by marc5180 View Post
    As Frank says, you need to take the temperature of the suction line and work out the superheat. This will tell you if the unit is short of refrigerant or if there is a blockage.
    If he said that he measured temperature at the coil at the bottom and the top, then he did somehow a SH measurement.
    One part will be at evaporating temperature, the other part will be superheated +/-10K. With the glide of R407c, his measurements are +/- normal.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. NRS BeerMaster cellar cooler
    By madfriday in forum Commercial
    Replies: 13
    Last Post: 22-06-2009, 09:24 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. sensible cooling duty of a cooler
    By samiam in forum Fundamentals
    Replies: 8
    Last Post: 16-02-2008, 05:49 PM
  4. cellar cooler fault.
    By fireblade in forum Commercial
    Replies: 12
    Last Post: 11-07-2007, 11:33 AM
  5. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •