Thread: r22 used in r407c rooftop unit.
-
18-07-2008, 02:41 PM #1
r22 used in r407c rooftop unit.
I have a rooftop unit that was accidentally filled with R22. It is labeled R407c, unit now will not work, what needs to be done to get the R22 out and back to R407c?
-
18-07-2008, 02:50 PM #2
Re: r22 used in r407c rooftop unit.
You do not need to take it out, it will work now better,
Not starting has nothing to do with the type of gas.
-
18-07-2008, 03:57 PM #3
Re: r22 used in r407c rooftop unit.
At least remove the c o cktail and fill it up with just R22, if you prefer that. Nothing else. POE oil is compatible with R22.
Last edited by NoNickName; 18-07-2008 at 03:57 PM. Reason: c o cktail is not a bad word. Unnecessary censorship
-
18-07-2008, 05:04 PM #4
Re: r22 used in r407c rooftop unit.
Unit has two compressors one tested w/R407C works , the one now w/ R22 runs but high presser line very hot compared to the R407c and the return line is warm. The air in duct is 75 f.
-
18-07-2008, 05:33 PM #5
-
18-07-2008, 06:18 PM #6
-
18-07-2008, 07:21 PM #7
Re: r22 used in r407c rooftop unit.
Does the system have both gases in it, R22 and R407C, ??
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
18-07-2008, 10:20 PM #8
Re: r22 used in r407c rooftop unit.
- Exactly, If half the evap coil is cold, its starved, go two turns counter clockwise. Adjust from there. If evap coil, and suction line are all same temp back all the way to the compressor, this would be a flooded condition- tighten the txv adjuster clockwise two turns. But none of this will matter unless there is a usable charge of 22 in the system-not over or under charged capice?
-
21-07-2008, 01:02 PM #9
Re: r22 used in r407c rooftop unit.
Leak. unit was pumped out and fixed pumped down and refilled w/r22
-
23-07-2008, 01:33 PM #10
Re: r22 used in r407c rooftop unit.
Leak. unit was pumped out and fixed pumped down and refilled w/r22
-
23-07-2008, 01:34 PM #11
Re: r22 used in r407c rooftop unit.
will poe oil work w/r22
-
23-07-2008, 01:35 PM #12
Re: r22 used in r407c rooftop unit.
no only r22 but the poe oil was not changed
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
SL/SB-400 Pump Down Procedures
By absolute-zero in forum TransportReplies: 1Last Post: 29-01-2008, 09:27 PM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
Charging a/c unit using R407C
By carlfoster in forum FundamentalsReplies: 22Last Post: 03-03-2007, 11:09 AM