    r22 used in r407c rooftop unit.



    I have a rooftop unit that was accidentally filled with R22. It is labeled R407c, unit now will not work, what needs to be done to get the R22 out and back to R407c?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: r22 used in r407c rooftop unit.

    You do not need to take it out, it will work now better,
    Not starting has nothing to do with the type of gas.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: r22 used in r407c rooftop unit.

    At least remove the c o cktail and fill it up with just R22, if you prefer that. Nothing else. POE oil is compatible with R22.
    Last edited by NoNickName; 18-07-2008 at 03:57 PM. Reason: c o cktail is not a bad word. Unnecessary censorship

  4. #4
    Join Date
    Jul 2008
    Location
    usa
    Posts
    6
    Rep Power
    0

    Re: r22 used in r407c rooftop unit.

    Unit has two compressors one tested w/R407C works , the one now w/ R22 runs but high presser line very hot compared to the R407c and the return line is warm. The air in duct is 75 f.

  5. #5
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: r22 used in r407c rooftop unit.

    Quote Originally Posted by just joe View Post
    Unit has two compressors one tested w/R407C works , the one now w/ R22 runs but high presser line very hot compared to the R407c and the return line is warm. The air in duct is 75 f.
    joe,

    Why was the unit serviced*?

    It could just be having the same symptons it had before it was serviced*.

    *(commissioned for you UK gents)

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: r22 used in r407c rooftop unit.

    Quote Originally Posted by just joe View Post
    Unit has two compressors one tested w/R407C works , the one now w/ R22 runs but high presser line very hot compared to the R407c and the return line is warm. The air in duct is 75 f.
    TXV probably need adjustment, as the bulb is selected for R407c and not R22.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: r22 used in r407c rooftop unit.

    Does the system have both gases in it, R22 and R407C, ??
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jun 2008
    Location
    South Carolina
    Age
    52
    Posts
    18
    Rep Power
    0

    Re: r22 used in r407c rooftop unit.

    Quote Originally Posted by NoNickName View Post
    TXV probably need adjustment, as the bulb is selected for R407c and not R22.
    - Exactly, If half the evap coil is cold, its starved, go two turns counter clockwise. Adjust from there. If evap coil, and suction line are all same temp back all the way to the compressor, this would be a flooded condition- tighten the txv adjuster clockwise two turns. But none of this will matter unless there is a usable charge of 22 in the system-not over or under charged capice?

  9. #9
    Join Date
    Jul 2008
    Location
    usa
    Posts
    6
    Rep Power
    0

    Re: r22 used in r407c rooftop unit.

    Leak. unit was pumped out and fixed pumped down and refilled w/r22

  10. #10
    Join Date
    Jul 2008
    Location
    usa
    Posts
    6
    Rep Power
    0

    Re: r22 used in r407c rooftop unit.

    Leak. unit was pumped out and fixed pumped down and refilled w/r22

  11. #11
    Join Date
    Jul 2008
    Location
    usa
    Posts
    6
    Rep Power
    0

    Re: r22 used in r407c rooftop unit.

    will poe oil work w/r22

  12. #12
    Join Date
    Jul 2008
    Location
    usa
    Posts
    6
    Rep Power
    0

    Re: r22 used in r407c rooftop unit.

    no only r22 but the poe oil was not changed

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Charging a/c unit using R407C
    By carlfoster in forum Fundamentals
    Replies: 22
    Last Post: 03-03-2007, 11:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •