    Blast Evap Fan Ice Build Up In Cowling



    Recently our company insltalled a large blast freezer the evap fans are high flow with 11kw motors we have a problem of ice droplets building up on the inside of the cowling which the fan blades nearly touch or rub on which inceases the load on the motor and trips the overload. Thankfully no blades have smashed yet! Just wondering if this has been a problem for anyone else? It has a water defrost but is not to long have looked at that and has an adequate dripping period. The ice droplets seem to form during the frezzing cycle.

    Thanks for any replies



  2. #2
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Re: Blast Evap Fan Ice Build Up In Cowling

    Hi matt, i have come across this prob before working at a site with several large cold rooms, to combat this we had to increase the number of hot gas de-frosts to about four a day, also being site based we had the luxury of doing weekly maintenance IE: getting in there and chipping the ice of, i know you can get heaters for this prob but don't know where, this has been raised before on this site so i'm sure someone will give you a better reply...Good luck mate..

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Blast Evap Fan Ice Build Up In Cowling

    Quote Originally Posted by matt watson
    The ice droplets seem to form during the freezing cycle.
    Is the water collecting on the cowling after defrost or during defrost?

    If you start off with a clean coil and cowling and then right after defrost the ice starts to accumulate in the cowling, it's usually due to the water droplets being pulled off of the coil (immediately after defrost when the fan starts).

    If this is the case, then the post defrost time for cooling the coil back down to operating temperature needs to be longer.

    Blast freezers operate with very high air velocities and they can certainly pull water that is not frozen off of the coil.
    If all else fails, ask for help.


  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Blast Evap Fan Ice Build Up In Cowling

    ITs all in the defrost cycle. Myself, I dont like water defrost in blast freezers from the point mentioned by US iceman.
    Try to increas the dripping time or run the fans backwards for a minut to dry the coils before it gets into cooling cycle again.
    Adjust the fans starting temp a few ° lower.

  5. #5
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    17

    Re: Blast Evap Fan Ice Build Up In Cowling

    When you experience this problem what type of ice is there ie flaky ice,as I had a similar problem and it was due to air infiltration which I solved with an air curtain.

  6. #6
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    17

    Re: Blast Evap Fan Ice Build Up In Cowling

    Check with the manufacturer if there is an option of defrost heaters for the fans cowling!

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Blast Evap Fan Ice Build Up In Cowling

    Quote Originally Posted by GXMPLX
    Check with the manufacturer if there is an option of defrost heaters for the fans cowling!
    That's a band-aid for a something else being wrong, in my opinion. To me this is almost like saying; if the fan cowling has ice on it the unit capacity is increased.
    If all else fails, ask for help.


  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Blast Evap Fan Ice Build Up In Cowling

    Matt.
    I aree with USIceman , extend drip time and coil chill time before fans start, what water is left on coil will freeze and not be dragged of by high velocity airflow, and attach to fan cowls.
    PS.. how did assignment go.
    magoo

  9. #9
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    17

    Re: Blast Evap Fan Ice Build Up In Cowling

    Quote Originally Posted by US Iceman View Post
    That's a band-aid for a something else being wrong, in my opinion. To me this is almost like saying; if the fan cowling has ice on it the unit capacity is increased.
    Not if ice buildup occurs during defrost!

  10. #10
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    17

    Re: Blast Evap Fan Ice Build Up In Cowling

    I would also check if the evap has fan delays, or they are working correctly because you could get water spray that quickly freezes when fans start.

  11. #11
    Join Date
    Mar 2008
    Location
    New Zealand
    Age
    39
    Posts
    6
    Rep Power
    0

    Re: Blast Evap Fan Ice Build Up In Cowling

    Thanks for the replies guys
    The defrost period is for 8 mins and i have watched it defrost and the fan blades do not sweat or defrost.
    The dripping period is for ten mins which i thought would be ample.
    I will clear the cowling amd monitor the build up.
    Thanks for the help

    Assessment went well cheers grunta!

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Blast Evap Fan Ice Build Up In Cowling

    Inform us about your progress so that we can learn from you
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Blast Evap Fan Ice Build Up In Cowling

    Quote Originally Posted by matt watson View Post
    Thanks for the replies guys
    The defrost period is for 8 mins and i have watched it defrost and the fan blades do not sweat or defrost.
    The dripping period is for ten mins which i thought would be ample.
    I will clear the cowling amd monitor the build up.
    Thanks for the help

    Assessment went well cheers grunta!
    you have mentioned the drip time, and the fact the moisture does not form on defrost, but you have failed to mention the fan delay that the evap has, is it time or temp initiated? how long/what temp? is it controlled by a klixon or a probe? what is its location?
    ...and she said "give it to me you big fridgie"

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Blast Evap Fan Ice Build Up In Cowling

    750 Valve made the same assumption I made, you better to it in my opinion temperature controlled and start the fans as soon you're sure they're completely frosted.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. iced up evap coil
    By wilks in forum Fundamentals
    Replies: 6
    Last Post: 31-08-2007, 09:15 PM
  2. Quest sandwich cooler evap?
    By The MG Pony in forum Commercial
    Replies: 6
    Last Post: 31-05-2007, 07:58 PM
  3. Replies: 10
    Last Post: 21-01-2007, 01:08 AM
  4. Blast Freezer Evaporators Selection
    By Mahmoud in forum Fundamentals
    Replies: 12
    Last Post: 21-09-2005, 04:31 PM
  5. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Replies: 13
    Last Post: 04-12-2003, 04:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •